Adiabatic equation infinite loop | on ElectriciansForums

Discuss Adiabatic equation infinite loop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Zdb

-
Joined
Mar 27, 2017
Messages
529
Reaction score
496
Location
UK
So I'm looking into the thermal constraints of every cable in my 2396 project.

I've used the adiabatic equation in a spread sheet and 99% of them are fine with the CPC I have selected.

However, there are a few really short circuits with very low earth fault loop impedance. Because of this the prospective fault current is really high and the adiabatic equation says I need a larger CPC.

Not a problem, I enter the adjusted values for the larger CPC into the spread sheet which automatically does the equation again....

Now because I've used a larger CPC, the loop impedance is even lower and the prospective fault current is even higher. It now says I need a larger CPC (again).

This seems to be an infinite loop.

Please can someone explain how I get around this?

Thanks
 
Quick thought - have you included a practical value for Ze in your calculator? The Ze will not be zero and you aren't making it any smaller, so it should converge ... he says hopefully :)
 
I think I will have to change cable type and use the minimum size conductor like Strima said.
 
If your using 0.1 seconds as T for say mcbs then there’s your problem if your disconnection time is below 0.1 seconds.
Get the let through energy from the manufacturer.
You’ll need to make sure k2S2 is equal to or greater than let through energy of the OCPD and using t=k2S2/i2 you’ll probably see that if your cable sizes comply, t being the maximum time before damage to the conductors and surrounding insulation starts to occur then your circuits will Probably comply.
 
Can you give an example that won't work for you ?

So the Zs is 0.2315764 ohms (3 metre circuit using 1mm/1mm singles).

Cmin ×nominal voltage = 218.5.

218.5 / 0.2315764 = 943.5331061 amps.

Looking at the curve for 6A type C 60898 on page 326 in the BYB it has to be 0.1s disconnection time.

Therefore the square route of 943.5331061 squared timed 0.1 = 298.3713663.

298.3713663 divided by my k value of 115 = 2.59mm minimum CPC required.

Like I said if I go up a size then use the equation again I will have go another size and so on and so on.

I guess I could have the wiring go round the room a couple of times to increase the Zs value therefore lowering the fault current :confused:
 
Yes as stated you need to find out the let through of the protective devices(the units aren't energy it's more like energy per ohm)
You would have an mcb with a bs fuse upstream so for higher pfc the fuse would blow first. Although with a normal sized lv transformer you would only get a maximum of 10kA or so? even if you were connected directly to the transformer due to the volt drop inside the transformer.
Also bear in mind the cpc size of the final circuit wouldn't affect the fault current because you're considering the case where the fault occurs directly after the mcb (ie worst case) so you would use zdb not zs.
For all other calculations eg disconnection time and volt drop the worst case is the far end of the circuit, but not for adiabatic.
Hope that helps!
 
So the Zs is 0.2315764 ohms (3 metre circuit using 1mm/1mm singles).

Cmin ×nominal voltage = 218.5.

218.5 / 0.2315764 = 943.5331061 amps.

Looking at the curve for 6A type C 60898 on page 326 in the BYB it has to be 0.1s disconnection time.

Therefore the square route of 943.5331061 squared timed 0.1 = 298.3713663.

298.3713663 divided by my k value of 115 = 2.59mm minimum CPC required.

Like I said if I go up a size then use the equation again I will have go another size and so on and so on.

I guess I could have the wiring go round the room a couple of times to increase the Zs value therefore lowering the fault current :confused:
Yes but your disconnection time will be less than 0.1 seconds ,you need the let through energy of the device from the manufacturer.
Also use the thermal constraints calculation I’ve already stated above.
Do not use 0.1 seconds.
Also your mcbs will be current limiting class 3 devices, you shouldn’t have an issue
 
Hi - in practice would you have a 1mm circuit that is only 3m long? Anyway, if pssc was 1000A and we use 100ms disconnect time then I2T is 100k. Looking at the Wylex B6 graph, it shows about 2k let through energy for 1kA which will give a very different result :) .

[ElectriciansForums.net] Adiabatic equation infinite loop
 
Also bear in mind the cpc size of the final circuit wouldn't affect the fault current because you're considering the case where the fault occurs directly after the mcb (ie worst case) so you would use zdb not zs
Just realised from wilkos post even that's wrong, it should not be calculated from the zdb, it should be the PFC which would be the maximum of the PSSC and the PEFC.
But still the final circuit would have nothing to do with the let through (energy per ohm)
 
What does the equation say when using 20mm conduit as the CPC?
 
I'm not quite sure how to work that out TBH.
All you need is the resistance of the conduit per meter, you can then work out your R1+R2 etc, change the K value on the adiabatic.

IIRC the minimum CSA of 20mm galv is around the 53mm area so you have plenty to play with.

Let me see if I can find the information I had.
 
How many people on here think the zdb+r1+r2 ie the Zs of the circuit in question is used in the calculation of the cpc size for adiabatic?
I feel like I'm the only one picked up the fundamental error (and wrong side error) the op described, and I'm not even a sparkly.
 
Hi - not sure I've understood correctly, but it may not be an issue in real life. Using the Wylex data from post #15 a B6 disconnects with I2T of about 10,000 on 10kA short circuit current (worst case, I should think). Plug that into adiabatic and 1mm2 is still ok. So not really something we have to think about every day ?
 
Th
How many people on here think the zdb+r1+r2 ie the Zs of the circuit in question is used in the calculation of the cpc size for adiabatic?
I feel like I'm the only one picked up the fundamental error (and wrong side error) the op described, and I'm not even a sparkly.
the zs of the circuit and resulting fault current is what is used as I in the equation
 
How many people on here think the zdb+r1+r2 ie the Zs of the circuit in question is used in the calculation of the cpc size for adiabatic?
I feel like I'm the only one picked up the fundamental error (and wrong side error) the op described, and I'm not even a sparkly.

That doesn't really make any sense.

The Zs would be even lower due to parallel paths.

All you need is the resistance of the conduit per meter, you can then work out your R1+R2 etc, change the K value on the adiabatic.

IIRC the minimum CSA of 20mm galv is around the 53mm area so you have plenty to play with.

Let me see if I can find the information I had.

I'll look into it. If you do have the info that would be great.
 
How many people on here think the zdb+r1+r2 ie the Zs of the circuit in question is used in the calculation of the cpc size for adiabatic?
I feel like I'm the only one picked up the fundamental error (and wrong side error) the op described, and I'm not even a sparkly.

Zs is used because a cpc which is suitable for conditions at the far end of the circuit can be assumed to be suitable at the supply end of the circuit.

Applying the adiabatic equation at the supply end as you suggest and at the load end results in a larger cpc from the load end calculation.
 
the zs of the circuit and resulting fault current is what is used as I in the equation
I'm saying that's wrong, as the worse case ie highest fault current will be when the fault happens close to the origin.
This is exemplified by the suggestions to increase the length of the circuit arbitrarily in order to reduce the necessary size of the cpc. If the fault happen 1m away from the cpc, the remaining 2m or 20m of the circuit are irrelevant.
That doesn't really make any sense.

The Zs would be even lower due to parallel paths.
Maybe it doesn't make sense at the moment, but by rating it Dumb, I'm not sure if that shows a good attitude to understanding whether you are making a serious and potentially dangerous mistake.i also notice it appears you are using cmin to calculate rather than the actual p(e)fc which is also incorrect.
Zs is used because a cpc which is suitable for conditions at the far end of the circuit can be assumed to be suitable at
I don't think that can be assumed, for example with a mechanical mcb the graph posted above clearly shows that not to be the case.
Applying the adiabatic equation at the supply end as you suggest and at the load end results in a larger cpc from the load end calculation.
Did not know that. Interesting, i will look at that. I would expect it to be either head end or the same.
 
Last edited:

Reply to Adiabatic equation infinite loop in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

For most domestic work the "standard circuits" in the On-Site Guide Table 7.1(ii) are all pre-checked for adequacy in these aspects, also there is...
Replies
3
Views
1K
  • Question
It's the same with any system, if you put poo in, you get poo out!
Replies
4
Views
1K
  • Question
Good point James. It would have been nice if the manual had mentioned which of the leads were being used for what though. It simply shows the LNE...
Replies
7
Views
522
While you can use the current/time plots for I2t, for the "instant" part of a MCB they are not really usable. MCB (and some MCCB) are...
Replies
4
Views
3K
  • Question
If they are installing 32A sockets they should have additional RCD protection which makes your problem academic.
Replies
2
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks