Hi guys,

any advice on what size of SWA should be burried for garage? Will be aprrox 15m long. Garage will have 6A lighting circuit 20A socket circuit and 32A power socket. Idealy 2core SWA as only one phase needed. IS 6mm ok or 10mm needed?

THX.
 
Are there any extraneous conductive parts?
What is the design load?
What type of OCPD and current rating?
No there are not. Design load of maximum 58A that means 13.34KW. OCPD 60947-3 probably 80amp as main switch (in the house) and then RCDo 63amp in mcb in garage.

By my calculations 10mm would be better. Correct?
 
Welcome to the forum mate.

If you answer the questions in post #2 then we can help you out more, maybe.
Also be aware of post #3 comment regarding Part P.
 
No there are not. Design load of maximum 58A that means 13.34KW. OCPD 60947-3 probably 80amp as main switch (in the house) and then RCDo 63amp in mcb in garage.

By my calculations 10mm would be better. Correct?

Quite a worrying response here. OCPD for the garage supply is the house CU main switch ?

As you are a new member could you state what qualification and experience you have, or pop it on your profile and set your profile to be able to be viewed publicly. This will help us help you best.
 
No there are not. Design load of maximum 58A that means 13.34KW. OCPD 60947-3 probably 80amp as main switch (in the house) and then RCDo 63amp in mcb in garage.

By my calculations 10mm would be better. Correct?

I didn’t think 60947-3 related to OCPDs, but I may be wrong.

Do you mean you are intending to use an 80A OCPD? In which case I don’t think 10mm will be suitable, off the top of my head 16mm may be better.
 
Quite a worrying response here. OCPD for the garage supply is the house CU main switch ?

As you are a new member could you state what qualification and experience you have, or pop it on your profile and set your profile to be able to be viewed publicly. This will help us help you best.
No it is not.
 

Reply to SWA size. 6mm ok or 10mm needed? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Sounds more positive.
Replies
8
Views
479
  • Question
Cheers guys, enjoyed reading all the responses. I'm an apprentice and it was a conversation that came up at work between two electricians...
2
Replies
43
Views
3K
  • Question
If your using 35mm or 50mm use 2 core SWA and use the armour as the earth, it'll cut down on price. I know people will comment on this but the...
Replies
10
Views
922
A picture paints a thousand words so here's an SLD showing my installation and some annotations to show the proposed relocation of the DC...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks