Hi,

New to the forum and I've got an issue in my house. I''mnot an electrician.

Our main RCD tripped last night and after investigating I've found the cause to be one of the sockets in the living room.
Testing the socket shows 50v across L+N, 230v across L+E, 30V across N+E.
Am I right in assuming there is a missing neutral connection?

The socket appears to be spurred off as there's only a single cable.
Maybe a junction box underneath the floor as I can't see where it's spurred from looking at the other sockets :(

Will I need to take my floor up?
 
You need to ring someone to be fair fella to test the circuit with an instrument suitable for the job, it could be several things, but a loose Neutral is one possibility.
 
Best advice Martin would be call an Electrician, as you say you are not an Electrician, playing about with this problem could be costly as you probably don't or won't know what you are looking for, could be a simple job but you won't know until a sparky looks at the problem, post your exact location one of the Members local to you may offer assistance.
 
Judging by the avatars Tel I'm the old fart, right you just wait mate.
i know you can take the banter, pete. you give enough out - like me. you know it's all in jest. no time for these prima donnas who can't take a joke. Up the Old Gits .
[ElectriciansForums.net] Tripped Socket - 50v
 
The RCD tripping could be a a complete coincidence with you finding this socket .
Yep. It may have been like that for a while.
It may be leakage somewhere else causing the trip.
Get someone in to investigate, generally.
…...an old git rather than a prima donna, maybe?
 
To be honest it's been around 2 years since we've last used that socket. So could be coincidence
I'm Stockton-on-Tees area.

I'm not fussed about it working as we don't use it, or should it be fixed to remove any potential issues.
 
:D
Yeah but the OP needs a spark :D

Ah go boil yer heid!


I'm Stockton-on-Tees area.

Too far for me, mate. Sorry.

I'm not fussed about it working as we don't use it, or should it be fixed to remove any potential issues.

It should be fixed.
If you have a loose connection somewhere there could be arcing... continuing heat damage to cables and a possibility of a fire.
Sorry to be the profit of doom.
 
It should be fixed.
If you have a loose connection somewhere there could be arcing... continuing heat damage to cables and a possibility of a fire.
Sorry to be the profit of doom.[/QUOTE]


You after making a quick buck, or what?
 

Reply to Tripped Socket - 50v in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
946
  • Question
They ought to be able to check for the voltage going completely off using one MCB off at a time to confirm that. That would be my assumption...
Replies
9
Views
820

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Thread starter

Joined
Location
North East

Thread Information

Title
Tripped Socket - 50v
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15
Unsolved
--
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top