I have an economy 7 boiler which has two temperature controlled heating elements. After 15 years they were replaced as they had started to heat inefficiently. Unsurprisingly they were covered in limescale.

I replaced them with new elements. The off peak element was placed on just over 50 degrees but kept on needing a reset so it was reduced to 45 degrees. After 6 months it blew up and the element needed replacing. It had split open and the fuse also blew.

I replaced both the elements with chrome elements. Same thing has happened again with the off peak element.

I am puzzled as to what is causing this and I am loathe to spend hundreds of pounds replacing them again.

I have one theory. My eco 7 off peak stays on all over the weekend. (Pls don't ask me why.) I think maybe that the element doesn't like staying on that much though I don't know how often elements check the temperature. I think that maybe the temperature control is malfunctioning meaning it heats up beyond what the temp is set at and then needs resetting as in the days before they blow it needs resetting a lot.

During the recent heat wave I hardly had it on and it was fine. As soon as it turned cold and had to some significant work it blew.

What can I do? Is it the electrics that are causing the problem and if so what action do I need to take.

The previous elements lasted for 15 years and worked great for 14.5 years without issue so I am puzzled why these new elements are breaking so quickly.

Thanks for any help or suggestions!

Rich
 
Do you not get 12 months warranty with the elements?
 
The plumber who installed them despite being a local, reputable firm has not been helpful in that regard. He said it would be hard to prove that the element was at fault.

Even if I got a refund of my £60 for the broken element it doesn't get me anywhere nearer to solving this problem.

It is strange that two consecutive elements have blown which would indicate it was not the element at fault. Or is it common that they blow like this?
 
My eco 7 off peak stays on all over the weekend.
It doesn't. There may be power to the element, but there is also a thermostat that controls the temperature. Once the water is heated (to whatever) the thermostat turns off the element, until the temperature drops.
When the element was changed, it would have been the best thing to chnage the thermostat as well.
 
Are you sure the thermostat is the correct length and type. I've come across the wrong length fitted, perhaps because that is what the plumber happened to have on the van, so it is not sensing the temperature in the correct place.
 
The most common cause of an element blowing open and splitting is dry running ie no water and excessive limescale build-up. You can pretty much rule out limescale if the plumber cleaned out the cylinder when the elements were replaced not long ago.

I'd also be wary of the quality of new items especially if the plumber is being unhelpful regarding a warranty claim, there's a lot of cheap rubbish on the market that's not fit for purpose. Usually a reputable wholesaler will happily entertain a warranty claim for a respectable brand name item if it was installed by a professional licensed plumber so I wouldn't accept him being 'unhelpful' if I were you.
 
I have an economy 7 boiler which has two temperature controlled heating elements. After 15 years they were replaced as they had started to heat inefficiently. Unsurprisingly they were covered in limescale.

I replaced them with new elements. The off peak element was placed on just over 50 degrees but kept on needing a reset so it was reduced to 45 degrees. After 6 months it blew up and the element needed replacing. It had split open and the fuse also blew.

I replaced both the elements with chrome elements. Same thing has happened again with the off peak element.

I am puzzled as to what is causing this and I am loathe to spend hundreds of pounds replacing them again.

I have one theory. My eco 7 off peak stays on all over the weekend. (Pls don't ask me why.) I think maybe that the element doesn't like staying on that much though I don't know how often elements check the temperature. I think that maybe the temperature control is malfunctioning meaning it heats up beyond what the temp is set at and then needs resetting as in the days before they blow it needs resetting a lot.

During the recent heat wave I hardly had it on and it was fine. As soon as it turned cold and had to some significant work it blew.

What can I do? Is it the electrics that are causing the problem and if so what action do I need to take.

The previous elements lasted for 15 years and worked great for 14.5 years without issue so I am puzzled why these new elements are breaking so quickly.

Thanks for any help or suggestions!

Rich

Does/did your system have a sacrificial anode(SA)? In certain water areas it can help enormously with corrosion.

The originals may have been high quality Incaloy or similar, very resistant to corrosion, coupled with a SA to give the long life.

I'm guessing the SA has corroded away, the new elements are cheapo (although you may have thought you were buying quality) and are only lasting a year.

Google galvanic corrosion and and sacrificial anodes.
 
Thanks for all your helpful replies.

I agree in retrospect it is suspicious that the plumber wouldn't provide me with the paperwork for the new elements. I asked numerous times before and after the fitting. I am writing formally to him.

The only thermostat in the system is that which is contained within the element. There is no separate thermostat.

I don't believe the system has a sacrificial anode(SA) nor were the original elements high quality Incaloy or similar. This is a shared ownership housing association block and everything was put together as cheaply as possible.

The first set of replacement elements looked identical to the originals. When the off peak replacement element split it wasn't covered in limescale unlike the originals. The chrome elements that replaced the first lot of replacements were slightly longer.

The system is a kernel direct plumbing unit produce code: 3396 installed in 2000. I can provide photos if helpful.

I've spoken to more of my neighbours and one of them said they had a similar problem with elements splitting. That neighbour didn't have a particularly solution beyond replacing the broken ones.

Can anyone suggest a good quality element to use this time?

Some of my neighbours have changed their set up completely, getting rid of economy 7, and moving to a pressure system. (Sorry not sure of the right term.) That's also an option.

Thanks again for your insights and suggestions.

Rich
 
The only thermostat in the system is that which is contained within the element. There is no separate thermostat.
I have never, ever seen that.

Inside the immersion housing for the element (under the top cover) there is a separate, removeable thermostat. The stat can be changed without draining the tank.

Please post a photo of the immersion connections.

[ElectriciansForums.net] heating element problems with economy 7
 
The blue bit is the thermostat and just pulls out.

If the stat is faulty, it may be powering the element too much. If you turn the red temp control you should hear it click as it switches on and off.
 
Thanks. I certainly think it possible that the stat has been faulty on the last two elements. Or at least unable to deal with the economy 7 being on all w/e. I started both elements at between 50 and 55 and as they reset gradually went down to 45. However by that time I think they had become faulty and the stat had completely failed leading to the splitting. That's my theory anyway.

Can you recommend a high quality element which the thermostat is less likely to fail?
 

Reply to heating element problems with economy 7 in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

As long as the heat input is greater than the heat losses from the container and the resistance is sufficient to limit the current to no more than...
Replies
2
Views
189
davesparks
D
Oh I see. I will check that one as well. Thank you!
Replies
5
Views
249

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top