So i am doing a new wiring job and all my cable is testing out fine. However the customer wants to put 2nd hand brass chandaliers up which i said could be an issue on IR tests if they are really old or damaged. Sure enough i have come to fit one and it tested at 0.96M live to neg. So i opened it up and the wiring appears to be either fairly new (blue and brown) or its been rewired. Either way each of the 15 arms is wired in singles back to the body where is was all together in connector strip. So i disconnected it all and metered the arms individually. Most tested around 3 to 4M. I removed one arm completely and it tested the same. I stripped out the wiring and pulled new in and reconnected the lamp holder. Still it was 3 to 4 M . So i removed the lamp holder and tested the new wires which were indeed fine. So i tested the lamp holder which showed the 4 M . I dissassembled the lamp holder so that it was litteraly the peice of bakerlite or plastic with two spring connections and it still tested at 4M between the terminals. I have wiped it washed it and dryed it and it doesnt change. In fact if i take the terminals off the plastic from edge to edge reads about 50M???

Any ideas whats happening here? Whatever is happening is happening to all the arms to varying degrees. The bit i stripped it down to is in the pic.

I am stummped as to how there is any connection on this part. Meter is testing other light fittings and they are reading well over 300M. It just seems to be these large 15 arm things.

[ElectriciansForums.net] What is going here then?
 
Either there is a deposit on the surface of the plastic insulator of the lampholders that your washing and drying did not remove, or the plastic is of inferior or degraded material that is conductive all the way through. Perhaps the surface is slightly porous and moisture has penetrated if they have been stored in a damp place. Try baking one out, or running a lamp in it for 24 hours, and see how it measures.
 

Reply to What is going here then? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Hello Brianmoooore, Thanks for yor reply - Sorry that I did not see your message until today - the Forum replies notification emails about your...
Replies
7
Views
616
  • Question
none at all.... and the rcd trips within specification... test button operational.... nothing to suggest there's a problem until you take the...
    • Like
Replies
2
Views
563

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top