So I have been working on a contract installing 10.5kw showers with B40 MCB's as specified by builders but occasionally a plot reports the shower tripping when having long showers. Hager don't do a 45A MCB but do a 45A RCBO but then its the cost....£££

The cable is ran in uninsulated studwork for around 9metres to the isolator and then around 4metres to go into loft and back down. Is there a way a I can justify a B50?

Any suggestions would be much appreciated!
 
who in their right mind wants a long shower? in, wet, soap, rinse, out for some beer. 5 minutes tops.
 
I'm with Post #2...
 
So I have been working on a contract installing 10.5kw showers with B40 MCB's as specified by builders but occasionally a plot reports the shower tripping when having long showers. Hager don't do a 45A MCB but do a 45A RCBO but then its the cost....£££

The cable is ran in uninsulated studwork for around 9metres to the isolator and then around 4metres to go into loft and back down. Is there a way a I can justify a B50?

Any suggestions would be much appreciated!

Cost ? £20 to do the job properly ?

No idea as only you know the routes and installation methods and the derating factors involved.
 
who in their right mind wants a long shower? in, wet, soap, rinse, out for some beer. 5 minutes tops.
Turn it on, run about for a bit you won't need a towel then, the builder specified the MCB let him sort it Mate, Although wonder how much he knows about electrics, probably specified from memory, oh that's what most shower installs consist of.
 
Turn it on, run about for a bit you won't need a towel then

What are you doing??????? I now have an image of you all wet, running around naked.... I need a 'Delete' button....
 
Hi - what size are the conductors? If you're using 6mm then 50A is a definite no. If there's no faults, I'd replace the mcb and see if it stops tripping.
 
Surely if the ‘builder’ specified the 40A MCB and that’s in writing in the design specs he gave you, then the builder is liable for the price of upgrading the MCB to a 45A RCBO. Just show him the cable/wattage calculations that show it needs the higher 45A MCB/RCBO, he then has no choice it to either downgrade the shower or upgrade the MCB/RCBO.
 
going back to the OP. this is a cunning plot to save water. as we all know, i times of low rainfall the country runs out of water, no hosepipes, and let your car/van look like something out of afganistan. fair play to the designer being conscienscious about saving water.
 
Does the existing consumer units have RCD protection with a spare way for the new circuit as it would be required anyway due to the circuit in bathroom and cables I presume within 50mm of the wall surface or metal stud work? Remember that with a standard 10.5kw resistive load shower you will not get overcurrent do your calculations based upon a B50 MCB.
 

Reply to 10.5KW shower 10mm stud wall query? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
i don't like showers anyway. bloody useless objects. water gets in your single malt and makes your smoke and your book soggy. give me a bath any...
Replies
19
Views
2K
N
The 50A Crabtree pull switches are far superior to anything else I've fitted. They have 2 openings at the top which the ends of the cable push...
Replies
24
Views
7K
chiplard
C
L
totally agree just left a post on another shower question ,have a look at page 31 table 2.3.1 installation referance methods , although we can...
Replies
7
Views
11K
nickblake
N
Thanks Howard. I think it is 50% as you say and I know in reality it will be fine and perfectly safe, I'm more trying to further my understanding...
Replies
7
Views
7K
E
Welcome @Geraldine you may be better off starting a new thread with more detail as Edd is no longer a forum member.
Replies
60
Views
80K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks