15.2kw range cooker has already been installed and a 10mm t&e run back to the Cu via this switch,(havnt seen cable route yet but I’m told on the phone it’s all in trunking and doesn’t pass through any insulation but will check this)apparently the previous spark that won’t connect it to the Cu said it need a 66A isolator!
He also left em an rcd to connect it to at the board even though it’s a split board,anyway I havnt been to the job yet but just wanted to check my diversity figures
I make it 26.8a without a socket included with the new isolator I’ll be installing,as always any and all advice is always greatly appreciated
[ElectriciansForums.net] Diversity calls check please........
[ElectriciansForums.net] Diversity calls check please........
[ElectriciansForums.net] Diversity calls check please........
[ElectriciansForums.net] Diversity calls check please........


[ElectriciansForums.net] Diversity calls check please........
 
Whats with the joining of them cpc's above the consumer unit? could he not afford a quid or two for an earth terminal block and do it properly? better still use the earth terminal in the actual CU?

Still at least he used fire rated glands on top, must have been left over in his installers kit from the trade show.

EDIT
on closer look it appears as if he has terminated the cpcs out of the consumer unit and by assumption means the line and neutral only go in to it? you can see the outer insulation stopping before the red glands with the inner cables exposed out of the unit.
Some labels would have helped too.
He could have used a screwdriver to pop them mcbs in line to, they would sit better, i do hate when BG boards do that. they are renowned for it.
 
Why have you included a picture of a rotary isolator? What role is that going to play? Please tell me it is instead of a 45A cooker isolator
On basis of that pile of crap that is a CU installation I wouldn't be surprised if the original person decided to use it as a light switch, you might laugh but I have seen it before!
 
Why have you included a picture of a rotary isolator? What role is that going to play? Please tell me it is instead of a 45A cooker isolator
That’s the pics that I’ve been sent over,far as I can workout that’s what he has used as the cooker isolator switch...
 
I love all the exposed single insulation going into the red glands, and the circuit labels are fantastic. I can't wait to see inside the CU!!!

I'd be more worried about the safety of the wiring than connecting a cooker to it..

What is that disconnected green wire?

Edit, I think the CPCs in the rotary isolator have been connected under the clamp screw rather than in the clamp where they should be.
 
That’s the pics that I’ve been sent over,far as I can workout that’s what he has used as the cooker isolator switch...
well if you are installing a new circuit in that CU you will need to sort out that mess on top of cables not being terminated properly on entry to the CU, with luck you can reuse them red glands and just get some t&e rubber inserts to go inside them. you cant tick the boxes on the Electrical Installation Certificate if you dont, given how poor it looks you might need to quote to put right other things you find inside! I would be wary of putting my name to the certificate with those things wrong. especially since you need to notify it aswell.
 
I love all the exposed single insulation going into the red glands, and the circuit labels are fantastic. I can't wait to see inside the CU!!!

I'd be more worried about the safety of the wiring than connecting a cooker to it..

What is that disconnected green wire?
No idea freddo, I had spotted the green wire, I havnt been there yet but after the conversation on the phone I asked the fella to send some pics of the cooker specs and what had been installed so far, I’ll be honest I’m a bit concerned after the picture of that Cu!
 
well if you are installing a new circuit in that CU you will need to sort out that mess on top of cables not being terminated properly on entry to the CU, with luck you can reuse them red glands and just get some t&e rubber inserts to go inside them. you cant tick the boxes on the Electrical Installation Certificate if you dont, given how poor it looks you might need to quote to put right other things you find inside! I would be wary of putting my name to the certificate with those things wrong. especially since you need to notify it aswell.
Thanks Gavin,yes I am going to ring him tomorrow as I’m not happy just adding a new circuit to that pile of crap to quote you ha ha thanks agian,
 

Reply to Diversity calls check please........ in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
"A catalogue of errors" would be the appropriate phrase here and I agree with Avo and James that HSE need to be involved rather than this forum...
Replies
4
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
5K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top