Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??
 
Thanks for the responses guys.
Yeh still a trainee. Passed my am2 3 weeks ago just finishing off my portfolio and told my employer id like to know how to design circuit and do all the calculations instead of just being told what to use as i want to learn as much as possible.
You should get yourself into the trainee area
 
Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??
A good video to get you started, there are plenty more, but this Bloke is one of the best, imo
 
Hi guys

I asked my work to help me wrap my head around calculating and designing for cable sizes. I watched chris kitcher on poo tube to get a better grip. My manager posed a scenario and ive tried calculating it but it doesnt seem right.

This is the set up.

There is an outbuilding 45m away that will have sockets and lights. Expect usage to be about 3kw.
It will be run underground but just buried no additional protection.

So i started with design current
Ib=p/v=3000/230 equals 13.04A

Protective device range
IN= 16A

Rating factor for ambient temp is roughly 30 degrees so this is equal to 1.00.
It greater than or equal to IN over rating factor equals 16/1.00 =16A

Reference method D so in table 4E4A to find anything near 16a means itll only be a 1.5mm conductor size.....

Where have i gone wrong??

Hi,

Im currently doing the 104 assignment for the hotel, cafe & pool.

Got this from my training provider which might help:

[ElectriciansForums.net] Designing and calculating
 
As no one has commented "Spoon, not only are you stunningly good looking but your observation skills are second to none.." on my post #5, I thought I'd better expand on it....
Check out reg 512.1.5
 

Reply to Designing and calculating in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Hi tssxrr, I am also doing my assignment on the same topics. would you mind sharing the documents which you have done so I will have rough idea...
Replies
1
Views
1K
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top