Morning chaps
Finally doing my 1st intake on the 19th!
It is for 14x flats and 1x L/L supply
SSEN are installing the new incoming supply and they said they are also supplying and fitting the Ryefield board and the main isolator
(I thought this needed to be done my me as a BNO??)
Anyways they apprantly want me to just installed the 14x switched isolators make of the 14x SWA sub mains and install the 150 x 150 trunking with the tails between my isolators and the meter
-and they will wire from the Ryefield into the supply side of meter
is this normal- i though the DNO stop at the head nowadays..
Also I do not think the client has choosen what company he will be using for the meters- what is a good safe spacing guide to space out the meters and isolators- I am going to try fit all 15x meters and 14 isolators on 2 rows wrapping around a 90degree corner
also am I right in saying the trunking above the head needs to be min 1300mm and max 1800mm high from floor?
How do people usually do their slots in the trunking for the tails going into the meter? -maybe 2x 25mm holes about 65mm apart then open these into one slot??
Cheers
J
Finally doing my 1st intake on the 19th!
It is for 14x flats and 1x L/L supply
SSEN are installing the new incoming supply and they said they are also supplying and fitting the Ryefield board and the main isolator
(I thought this needed to be done my me as a BNO??)
Anyways they apprantly want me to just installed the 14x switched isolators make of the 14x SWA sub mains and install the 150 x 150 trunking with the tails between my isolators and the meter
-and they will wire from the Ryefield into the supply side of meter
is this normal- i though the DNO stop at the head nowadays..
Also I do not think the client has choosen what company he will be using for the meters- what is a good safe spacing guide to space out the meters and isolators- I am going to try fit all 15x meters and 14 isolators on 2 rows wrapping around a 90degree corner
also am I right in saying the trunking above the head needs to be min 1300mm and max 1800mm high from floor?
How do people usually do their slots in the trunking for the tails going into the meter? -maybe 2x 25mm holes about 65mm apart then open these into one slot??
Cheers
J