Lewden 100a switch fuse burnt out | on ElectriciansForums
Guest viewing is limited

Discuss Lewden 100a switch fuse burnt out in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 3, 2015
Messages
85
Reaction score
58
Location
United Kingdom
[ElectriciansForums.net] Lewden 100a switch fuse burnt out
[ElectriciansForums.net] Lewden 100a switch fuse burnt out
Has anyone had problems with this switch fuse??? I went to one last year which was warm to the touch, so I changed it for an Amd3 metal one. I found this one today burnt out, close call. The screw terminals were tight - the source of the heat looks to be the contact inside the switch. This one was less than 5 years old.
[ElectriciansForums.net] Lewden 100a switch fuse burnt out
 
The terminals are a bit pathetic on these and the Twist Wiggle And Twist method and a large slotted screwdriver is essential to get these terminals tight. I have been to several where the terminals have been loose. IIRC the screw is made of a different metal to the terminal which is never a good idea, but I could be wrong.
 
I wonder which started first, the contact erosion could have started after everything got hot from a loose cable connection and the switch contact moved position when the plastic melted/burned.

I have seen other problems with the metal Lewdon 100A switch fuses, went to look at a fault at a pub/restaurant that only had a single phase supply, a large distribution board was connected via the switch fuse. This was new and had been fitted 6 days earlier by another company as the old switch fuse burnt out. I was called to 'check the electrics' as the cutout fuse had blown. Looking in the new switch fuse the connections were all loose and one of the new 25mm tails was clearly heat damaged. I don't believe the terminals were left loose by the installer but had worked loose from the heavy thermal cycling. The brass terminals the installer fitted the tails to in the 4 100A blocks, including the 2 new ones he fitted to cut out the heat damage from the outgoing tails were all tight.

With the power on I measured 141A being drawn and the wiring and fuse soon started getting hot.
 
Did you get a chance to clamp the cable and see whay kind of power it was drawing?

No I didn’t, but that’s a good call. I’ll put the clamp meter on in max/min mode and see what it gets to. It was an all electric 4 bedroom house (underfloor heating throughout) on a cold frosty morning with the lady at home running appliances. Could be a big number.
 

Reply to Lewden 100a switch fuse burnt out in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Oh definitely, the amount of tails that I come across in consumer units barely nipped up is staggering, I always tighten them, wait a minute, give...
    • Like
2
Replies
27
Views
2K
  • Question
Ah OK, that makes sense. Thank you Avo.
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top