gazdkw82

-
Arms
Joined
Aug 2, 2013
Messages
1,912
Reaction score
739
Location
leicester
Where can I find the max Z's value for a BS3871, type 3, 32A MCB?

Iv had a look through BS7671 and done some searching online but I cannot find it. IV found some tables with listed Zs values for a 3871 but I have no idea where they originate from or how old
 
It's not required. It asks for the max Zs values listed in BS7671.
But the tables for BS3871 are not listed within BS7671 which already have Cmin applied as of the 17th Amdt 3.

So to ensure the circuit complies with current regulations you would have to apply Cmin and then 80% to take into account thermal compensation.

How is Cmin applicable to any works you carry out on an existing circuit?
 
Upvote 0
But the tables for BS3871 are not listed within BS7671 which already have Cmin applied as of the 17th Amdt 3.

So to ensure the circuit complies with current regulations you would have to apply Cmin and then 80% to take into account thermal compensation.

How is Cmin applicable to any works you carry out on an existing circuit?

Bs7671 does not have the rule of thumb applied. Onsite guide does. The minor works is asking for values from BS7671, therefore it's asking for values without the rule of thumb applied.
 
Upvote 0
Bs7671 does not have the rule of thumb applied. Onsite guide does. The minor works is asking for values from BS7671, therefore it's asking for values without the rule of thumb applied.
I'm not talking about the rule of thumb, I'm talking about Cmin.
 
Upvote 0
With most faults on an installation, the current is proportional to the supply voltage.

The intention of using Cmin when calculating the allowed loop impedance, is to ensure that sufficient fault current is available for the protective devices to operate within the required disconnection times at the minimum voltage the DNO is allowed to deliver - currently 6% below nominal.
 
Upvote 0
I spoke with guardian today. They informed me that R1+R2 must be taken from the point of circuit origin.

I have emailed all higher management/technicians and informed them that this is the standard requirement for testing.
 
Upvote 0

Reply to Maximum Zs values for BS3871 in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
Generally speaking local earthing will rarely be below a couple of ohms, so in parallel with a TN-S sub-ohm value will make little difference...
Replies
4
Views
609
  • Question
BS3871 type 3's have a similar shaped operating curve to BS60898 type C's. Any fault that will meet the disconnection time of 5s (for 63A...
Replies
5
Views
2K
A bit of a classic instance of too much information on the Test Sheets imo (plenty of others). Hard to explain to a client if its not just a case...
Replies
4
Views
3K
  • Question
It is a combined RCBO/AFDD so would make sense its rated the same. One of the reasons I was asking is that it didn't auto fill when filling out my...
Replies
4
Views
6K
  • Question
Definitely the radial, we were talking about and discussing different size cables for the different circuits. I have made some amendments to my...
Replies
12
Views
9K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks