I think I may have asked this question a while ago but not sure on what the answer was and it's come up again at our monthly tool box talk.

When doing a Minor works for an additional spurred socket or extra light fitting on a circuit, should the R1+R2 measurement be taken from the protective device or the socket/fitting you have spurred from?
 
Some instances it's completely unavoidable. For example, opening trunking to that enclose numerous circuit wiring. You may isolate the circuit your working on but all the other circuit wiring is live.

I've opened trunking before to be greeted with bare copper ends.
That is very worrying.
I can see that there are going to be many revelations in that workplace that are going to bother your conscience.
 
Upvote 0
just because it's been mentioned a few times and not corrected - a Zs test does not confirm that the CPC is earthed correctly and can not be relied on.
The simple reason is that the apparent earth may be provided via bonding for example an under sink water heater through a metallic pipe.
Any alterations to the plumbing system can render that useless straight away.
 
Upvote 0
I spoke with guardian today. They informed me that R1+R2 must be taken from the point of circuit origin.

I have emailed all higher management/technicians and informed them that this is the standard requirement for testing.
 
Upvote 0
Well this is just getting confusing now. It really is a grey area.

Our electrical technician has said the contractors we use onsite have said they have spoken with NICEIC and they have said all they need to do is test the leg they have just installed.

I phoned the NICEIC myself and they said it depends on what work has been done. If we are spurring off the load side of a spur then we just test that little section and make a note on the test sheet.

IV just had an email response from a email I sent to guardian over a week ago.

Below is the response. Contradicts what they told me on the phone.

[ElectriciansForums.net] Minor works R1+R2 measurement
 
Upvote 0
Yes. It's highly frustrating. There must be some literature that settles this somewhere.

I don't see how you can be sure the cpc goes back to the MET without an R1+R2 of the entire circuit

It is clear and if it is not a cpc or a R2 unless it is connected to the MET. If it is not it is just a bit of copper in a cable.
 
Upvote 0
I personally think that you basically have to be satisfied that the r1+r2+ze complies with ADS requirements. Enough to sign your name to it on the certificate. in an installation that is well controlled you could demonstrate compliance by using the documentation available from previous dead testing plus your new partial testing using notes on the certificate to explain your route to compliance so that the documentation as a whole represents the situation.
If the installation has had evidence of unprofessional modifications etc then it would not be professional to alter it without a full test.
As with everything in life you have to follow the rules unless there's a reasoned/risk assessed justification not to. If you can do the risk assessment then you can defend it in court;)
 
Upvote 0
How about measuring R2, with a wander lead , between the furthest part of the new circuit and the earth terminal of a socket that is close to the consumer, but definitely on another circuit? R2 value will be high, by the R2 of the socket circuit, but will at least confirm the continuity of the cpc.
 
Upvote 0
r1 + r2 is also measured for initial verification. Ze + (r1 +r2) is approximately equal to the expected Zs. Ensures that the circuit is safe to energise before "live" Zs reading is taken. Apparantly is acceptable to calculate r1 + r2 from Zs-Ze when carrying out future testing (advice from NICEIC) sounds a bit wrong to me !
 
Upvote 0
r1 + r2 is also measured for initial verification. Ze + (r1 +r2) is approximately equal to the expected Zs. Ensures that the circuit is safe to energise before "live" Zs reading is taken. Apparantly is acceptable to calculate r1 + r2 from Zs-Ze when carrying out future testing (advice from NICEIC) sounds a bit wrong to me !
R1+R2 you mean? r1,r2 and rn are an end to end resistances of a RFC conductors, yes I'm a pedant, before you comment.
 
Upvote 0
r1 + r2 is also measured for initial verification. Ze + (r1 +r2) is approximately equal to the expected Zs. Ensures that the circuit is safe to energise before "live" Zs reading is taken. Apparantly is acceptable to calculate r1 + r2 from Zs-Ze when carrying out future testing (advice from NICEIC) sounds a bit wrong to me !
Calculating R1+R2 is only acceptable at the design stage using known values of resistance and the applicable correction factors for instances like change in temperature etc etc.
It’s must certainly wrong to subtract the Ze from Zs to come up with a value to be written down on a certificate/report.
 
Upvote 0
r1 + r2 is als
R1+R2 you mean? r1,r2 and rn are an end to end resistances of a RFC conductors, yes I'm a pedant, before you comment.
I stand corrected (well sit down corrected to be precise)

o measured for initial verification. Ze + (r1 +r2) is approximately equal to the expected Zs. Ensures that the circuit is safe to energise before "live" Zs reading is taken. Apparantly is acceptable to calculate r1 + r2 from Zs-Ze when carrying out future testing (advice from NICEIC) sounds a bit wrong to me !
Calculating R1+R2 is only acceptable at the design stage using known values of resistance and the applicable correction factors for instances like change in temperature etc etc.
It’s must certainly wrong to subtract the Ze from Zs to come up with a value to be written down on a certificate/report.
I agree, pointless to "back" calculate R1 + R2
 
Upvote 0
r1 + r2 is als

I stand corrected (well sit down corrected to be precise)

o measured for initial verification. Ze + (r1 +r2) is approximately equal to the expected Zs. Ensures that the circuit is safe to energise before "live" Zs reading is taken. Apparantly is acceptable to calculate r1 + r2 from Zs-Ze when carrying out future testing (advice from NICEIC) sounds a bit wrong to me !

I agree, pointless to "back" calculate R1 + R2
als?
 
Upvote 0

Reply to Minor works R1+R2 measurement in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

  • Question
There could also be a completely unsuitable junction box embedded within the wall and tiled over or just cables in choc blocks in old accessory...
Replies
6
Views
831
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
  • Question
Thank you bud. I’m loving this forum already being in communication with like minded individuals like yourself who can share knowledge.
Replies
4
Views
2K
  • Question
But a plug ‘top’ BS1362 fuse is not protecting fixed wiring is it, so perhaps not a good analogy.
2
Replies
35
Views
8K
  • Question
Now it looks like I copied you and showed no originality! 😞
Replies
15
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Courses

This is the main Electrical Courses at ElectriciansForums.net. Find local recommended electricians courses. Avoid training "company" scams. Always go view the training centre before booking any electrical courses.
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks