I have been asked to connect a 9kW kiln to the consumer unit.

The consumer unit is in the garage and the kiln will also be in the garage.

All the cable will be surface mounted, probably in conduit.

It's a steeple series E consumer unit with spare ways on the non-RCD side and no spare ways on RCD side.

I had decided to fit a 40A MCB on the non-RCD side into a standalone RCD but having thought about about it, does it require RCD protection? I'm so used to making sure everything has RCD protection but I can't see that this meets any of the requirements to do so.

Also, I dont think there are any RCBO's that fit the steeple series E board are there? lastly, I have assumed there are no spare ways on the RCD side from the picture below (I haven't visited yet), what do you think? Cheers all :)

[ElectriciansForums.net] Does this require RCD protection?
 
From the information, you have supplied, it either does not require RCD protection, or can be designed so as to not require RCD protection.
Looking at the picture, it appears that it could be possible to change the busbars so that an extra circuit could be added to the RCD, though that might then exceed the RCD’s rating.
 
As previously said you do not need a RCD specially when loading a kiln with wet clay! It may be worth considering putting it on it's own switch fuse due the the amount of load it will add to the install for long periods.
 
As previously said you do not need a RCD specially when loading a kiln with wet clay! It may be worth considering putting it on it's own switch fuse due the the amount of load it will add to the install for long periods.
Are you thinking specifically about the max demand of all the circuits in the CU with regards the limit of the 100A main switch?
 
Being a 643 times bitten person, I'd want the kiln to have RCD/RCBO somewhere. Just thinking it might not be the best maintained and tested bit of kit.
 

Reply to Does this require RCD protection? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
641

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top