Hi again!

Which value is best to record in a certificate or report, a max measured or a calculated Zs?

I know Sparkies who do it both ways, but personally I take measured values at all the points of utilization to find the highest, then I calculate Ze+(my highest R1+R2) for the circuit and then I compare the max measured and my calculated values and record the highest of the two on the certificate.

Any thoughts?
 
If safe to measure Zs and I've measured it, I put the highest measured value down. If not safe to measure, I calculate it from Zdb + (R1+R2).

Edit: if it's a TT system and (for example) Ra = 100Ω and the board is at the origin (so Ze = 100Ω ish) but Zdb goes down to, say, 20Ω once bonding is connected, I would use Zs = 20 + (R1+R2).

(tin hat on)
 
If safe to measure Zs and I've measured it, I put the highest measured value down. If not safe to measure, I calculate it from Zdb + (R1+R2).

Edit: if it's a TT system and (for example) Ra = 100Ω and the board is at the origin (so Ze = 100Ω ish) but Zdb goes down to, say, 20Ω once bonding is connected, I would use Zs = 20 + (R1+R2).

(tin hat on)
But would a calculated value not be a truer reflection of the circuits prospective max Zs i.e. with no parallel paths at play
 
Yes, hence the tin hat. :)

In the example of a TT system, though - unless you're using a 300mA or 500mA RCD for fault protection, it's not going to make much difference.

Bonding should be in place for ADS. When you measure Zs, bonding is in place.

If you measure Zs for some circuits (sockets, say), with values all around the 20-odd ohms mark, and you decide to use "proper" Ze + (R1+R2) for those you calculate Zs for, they'd be around the 100-odd ohms mark, and it would look... odd. You'd not really be comparing like for like (between circuits).
 
Yes, hence the tin hat. :)

In the example of a TT system, though - unless you're using a 300mA or 500mA RCD for fault protection, it's not going to make much difference.

Bonding should be in place for ADS. When you measure Zs, bonding is in place.

If you measure Zs for some circuits (sockets, say), with values all around the 20-odd ohms mark, and you decide to use "proper" Ze + (R1+R2) for those you calculate Zs for, they'd be around the 100-odd ohms mark, and it would look... odd. You'd not really be comparing like for like (between circuits).
In your TT example the highest reading would always be the calculated value so that would be method I would use for all circuits, so I would be comparing like for like wouldn't I?

Also with regards to your comment on bonding, what would happen if the utility pipe were upgraded to plastic and the parallel path previously giving you 20 ohms disappeared?

Oops I havent got a tin hat!:(
 
Yes, these are points I had thought of, and you're right (I almost added a "PS" along those lines but assumed you would respond as you have).

If, ultimately, the presence or absence of bonding would make a difference between requirements for ADS being met or not (let's say fault protection for a particular circuit is via a 500mA RCD only, and Ra>100Ω, but with bonding Zdb is <<100Ω) then this would require a different response, depending on whether it's a new installation or an inspection and test.
 
Hi again!

Which value is best to record in a certificate or report, a max measured or a calculated Zs?

I know Sparkies who do it both ways, but personally I take measured values at all the points of utilization to find the highest, then I calculate Ze+(my highest R1+R2) for the circuit and then I compare the max measured and my calculated values and record the highest of the two on the certificate.

Any thoughts?
Measured.
It’s a schedule of test results, not a schedule of calculations.
 
Record the measured value. One of the reasons we record the values is so that subsequent EICRs and other testing can be compared to the original test results to track any deterioration in the circuits.
But wouldn't any deterioration in the circuit be identifiable in the compared R1+R2 measured readings?
 
[ElectriciansForums.net] Measure or calculate your Zs?
For initial verification The regulations say that where the effectiveness of the protective measure has been confirmed at a point located downstream of an rcd the protection of the installation downstream from this point may be proved by confirmation of the continuity of the protective conductors.
An R1+R2 test confirms this.
Where the rcd is tested and satisfies fault or additional protection then further testing is not nessicary according to the above NICEIC tech article.
If there’s no rcd and the circuit relys upon an ocpd for fault protection then the zs shall be confirmed by the appropriate measures.
643.7.1

Take it how you will I’d still just calculate or measure the Zs personally and write it in the appropriate column on the schedule of test results
A controversial point maybe?
 
Last edited:
See, I don’t understand this urge to fill in all the boxes?
The whole point of the schedule is to record the values obtained from tests, that you’ve conducted (hence the name).
You don’t get a gold star or a Brucie Bonus for filling in all the boxes. Unless of course you calculate the R2.

The other thing is, on some circuits the measured value for Zs will be considerably lower than the calculated value due to parallel paths.
For instance, boiler circuits or immersion heater circuits, all those copper pipes and bonding conductors will lower the Zs.
 
My recollection from the 2391 is that zs should be measured when safe to do so and calculated otherwise.

The interpretation was that sockets would be measured using an adaptor. Pretty much everything else calculated.
 

Reply to Measure or calculate your Zs? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
218
  • Question
As previously posted, almost certainly due to differences in readings obtsined with high and low current measurements on the meter, low current...
Replies
10
Views
2K
OLDBOY
O

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top