Quick query I’m hoping someone can clear up. Im just looking at an example of a schedule of test results in a book I’m studying and I’ve come across an example I don’t understand. A lighting circuit protected by a 6amp 60898 Type C (Ref Method 100) using 1.5/1.0 T&E is measuring out R1+R2 at 0.12. The circuit is approx 38 metres in length.

Working off the calculation that the R1+R2 should be around 30.20 ohms x 38 / 1000 = 1.14. I can’t understand how they have reached this figure. There may be a shaver socket on the circuit as it mentions one of the circuits does have a shaver socket (but it doesn’t specify which), but I don’t know if that would impact anything? It could just be the test reading has been mis-typed but it would be great to get to the bottom of it by learning something new. Just wondering if it’s anything obvious to the vast sea of experienced helpful heads out there.

Thanks again.
 
What is the book and in what context are you studying it?

I believe R1+R2 for a 1.5/1.0 cable is 0.03 ohms per metre which would make it 1.14. This suggests it is a typo in the book.
 
What is the book and in what context are you studying it?

I believe R1+R2 for a 1.5/1.0 cable is 0.03 ohms per metre which would make it 1.14. This suggests it is a typo in the book.
1.14 @ 20 deg. C, so probably 1.2 @operating temperature. typo.
 
Geez, thanks guys, good to get your advice. The book is Practical Guide to Inspection, Testing & Certification of Electrical Installations (18th ed.) by Christopher Kitcher.

These books can cause more questions than give answers when they contain errors like that. It's a bit annoying sometimes for someone trying to learn. Thank god for forums like this.

[ElectriciansForums.net] Rather Low R1+R2 Query

[ElectriciansForums.net] Rather Low R1+R2 Query
 
Also goes onto show that the Zs is incorrect too. He has just added the 0.63 Zdb reading to the R1 + R2 therefore extending the error across too lol. Look at the relationship between Zdb, R1+R2 and Zs's. They never work quite like that when measured. Goes to show why you should always really take a Zs!! Maybe Chris Kitchener threw that in there to see if you'd notice......NOT haha. Anyway, we'll done OP, you are a sharper student than many that you noticed it. Good on you mate!!
 

Reply to Rather Low R1+R2 Query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

  • Question
what is testing? is it a male hormone?
Replies
7
Views
6K
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K
Thanks, that is useful clarification. Yes, strictly speaking all AC measurements for protection, etc, are |Z| = sqrt(r^2 + x^2) as it is only the...
Replies
9
Views
9K
  • Question
Thanks. This really has been useful. Can definitely see the pitfalls to relying on live Zs. I think I'll get cracking on writing up some...
Replies
15
Views
2K
  • Question
Hi Guys, I'm doing my Level 3 C&G design project and just have a few design related queries which i am so far struggling to find clarity on...
Replies
0
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks