im hoping I’m doing something stupid so please chip in with any help.
Recently upgraded my 10 year old Metrel meter with a Fluke 1664. So on the metrel doing phase rotation test on the screen it comes up L1 L2 L3 and tells you it’s correct or not, if its not it actually tells you which is incorrect.
So today I thought I’d try the Fluke, so connected the leads and it says 123 on the screen great I thought, so then tried it in a wrong connection and it comes up 321 on the screen, then tried the third combination and it says 123 again.
Does not read L1,L2,L3 anywhere.
Is this correct on a fluke? Or am I missing something?.
 
Quick guide shows 1 2 3;


[ElectriciansForums.net] Fluke Phase Rotation Testing help
 
im hoping I’m doing something stupid so please chip in with any help.
Recently upgraded my 10 year old Metrel meter with a Fluke 1664. So on the metrel doing phase rotation test on the screen it comes up L1 L2 L3 and tells you it’s correct or not, if its not it actually tells you which is incorrect.
So today I thought I’d try the Fluke, so connected the leads and it says 123 on the screen great I thought, so then tried it in a wrong connection and it comes up 321 on the screen, then tried the third combination and it says 123 again.
Does not read L1,L2,L3 anywhere.
Is this correct on a fluke? Or am I missing something?.
Don't think you are missing anything Mate, other than maybe reading the instructions a bit more thoroughly, we have all been there.
 
Don't think you are missing anything Mate, other than maybe reading the instructions a bit more thoroughly, we have all been there.

I think I am going to have to read them, seams to have a whole different way of reporting to my old set.
Progress I guess.
Thank you for the reply
 
I think I am going to have to read them, seams to have a whole different way of reporting to my old set.
Progress I guess.
Thank you for the reply
N o worries Mate like I said we are all, or most of us guilty of said sin of not RTFM
 
According to the instructions the only results it gives are;

123, which means correct rotation
321 which means incorrect
--- which means insufficient voltage, presumably 1 or more leads not connected or phases missing.

1,2,3 means correct, (clockwise) not necessarily L1,L2,L3, It could also be L2,L3,L1 and the same with incorrect.

I think the O.P might think the meter is Smarter than it actually is.
 
There is no "correct" or "incorrect" when it comes to phase rotation...
You're simply referencing what you're reading against something else (when adding to an install), or something that's been previously measured and you're replacing a piece of equipment.

I'll get a 'disagree' for that... but if you are adding to a huge installation and its reading 132, instead of 123... would you say the entire site was incorrect and needed reversed?
 
There is no "correct" or "incorrect" when it comes to phase rotation...
You're simply referencing what you're reading against something else (when adding to an install), or something that's been previously measured and you're replacing a piece of equipment.

I'll get a 'disagree' for that... but if you are adding to a huge installation and its reading 132, instead of 123... would you say the entire site was incorrect and needed reversed?

Fun fact, most of the liverpool area runs in the wrong direction from the rest of the country.

Happened because of a mistake made years ago when we were transitioning from DC. It' s been the wrong way for so long now correcting it is impossible. The DNO are just aware of it an work around it.
 

Reply to Fluke Phase Rotation Testing help in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

Having some issues with my companys fluke 1662/1663 tester. Zeroing 2 leads for continuity test we get the value 0.08 which is expected. The issue...
Replies
0
Views
209
  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top