Hi all,

When wiring a kitchen and the customer is buying a separate cooker and hob, which combined has too high a load for a single 6mm,
Do you wire two separate circuits with a 6mm for each or one larger cable and have both on same circuit?
 
I tend to get the specifications from the client and decide. I've done two kitchens this year and one had 3 new circuits (10mm for hob and 2 x 2.5mm, one each for fitted oven and microwave) whilst the other had one (10mm for range cooker).

And as @dinger809 says... local isolation for each.
 
I tend to get the specifications from the client and decide. I've done two kitchens this year and one had 3 new circuits (10mm for hob and 2 x 2.5mm, one each for fitted oven and microwave) whilst the other had one (10mm for range cooker).

And as @dinger809 says... local isolation for each.
and a fat wallet to pay for the electrickery.
 
Hi all,

When wiring a kitchen and the customer is buying a separate cooker and hob, which combined has too high a load for a single 6mm,
Do you wire two separate circuits with a 6mm for each or one larger cable and have both on same circuit?

Redo you calculations and don't forget diversity. It is very likely the cooker and hob can both go on a single 4mm cable on a 32 amp MCB.
 
Yes. There is no requirement for isolators at all.

But assuming the customer requires it there is no reason why one isolator cannot switch both appliances. After all if the cooker and hob were not separate you would only use one isolator. You can get dual outlet cooker connection units too. You would also only need one cable and it would most probably be OK with a 4mm cable on a 32 amp MCB.
 
@Chris , you should also take into account manufacturers instructions (nearly all the oven type appliances I've connected up have specified ratings for the OCPD they are connected to) and consider the general guidance in the regs about splitting the installation to minimise inconvenience in the event of a fault (as an example, the first kitchen I did this year suffered a failure of one appliance which resulted in the RCBO supplying it tripping - it wasn't an urgent issue as the hob and second oven had their own supply so the home owner was able to cook).
 
Trouble is manufacturers instructions can be wrong as in this example here. This was with a B & Q oven.

[ElectriciansForums.net] Cable for cooker andseparate hob?
 
Trouble is manufacturers instructions can be wrong as in this example here. This was with a B & Q oven.

View attachment 48121

So in that case I would use what I like to call 'common sense' and install a 20A DP isolator near the device (so as to comply with the double pole isolation requirements) and supply it from a 16A MCB/RCBO so as to comply with the 16A fusing requirements.

In the event of something going wrong, you have then complied with the manufacturers requirements of double pole isolation and fusing. Thus your backside is covered.
 
Yes. There is no requirement for isolators at all.

But assuming the customer requires it there is no reason why one isolator cannot switch both appliances. After all if the cooker and hob were not separate you would only use one isolator. You can get dual outlet cooker connection units too. You would also only need one cable and it would most probably be OK with a 4mm cable on a 32 amp MCB.
You're welcome to try and Isolate mine Mate. 4mm 2 is no good need something heavier, 70mm 4 core would just about manage it, providing you get a decent swing at it.
 

Reply to Cable for cooker andseparate hob? in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I actually did it with a 4 core 4.0mm swa last week!
Replies
12
Views
737
  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
655

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top