Does anyone know if its acceptable to have the ocpd of a radial circuit serving only single sockets higher than 32A ?

2 x 6mm would be the most a socket could take so probably 40A OCPD (singles in trunking).
 
How’s the vicar doing his teas and coffees just now? Extension leads off extension leads probably.
Individual radials for highest power items. 2.5 rfc for less with regular 32A ocpd.
Easier to install, easier to terminate. And 2.5 costs less than 6mm
 
Does anyone know if its acceptable to have the ocpd of a radial circuit serving only single sockets higher than 32A ?

2 x 6mm would be the most a socket could take so probably 40A OCPD (singles in trunking).
Question is, why would you want to? Appendix 15 BS7671
 
That is a point I am getting frustrated with most s/o these days. The termination point is very reticent even properly accepting 2 x 2.5 leading to a difficult insertion. Curve, Hamilton, and the cheaper brands all seem to have a crap termination point. I took 3 boxes of sockets back last week and got some MK instead at screwfix. I don't think they are fit for the purpose. Bring back the good old days where you had a half inch round hole (ok slight exaggeration!) to double the cables over in. Try doing that now with the modern sockets. I had a trainee working with me after half an hour he could not terminate the sockets properly. I had to exchange them.
I remember when I started out in the 80's using contactum with large bellmouth terminals that could take 2 x 6mm cables.
 
How’s the vicar doing his teas and coffees just now?
[ElectriciansForums.net] BS 1363 socket circuit
 
9.3kw
Was waiting for why. Basically there is 5 plug in appliances (totalling 9.3 KW including tea urns, coffee machines, fridge, 2x kettles which a vicar needs to be on simultaneously, once in a while. One circuit would be easier to run than two.
9.3KW
Does anyone know if its acceptable to have the ocpd of a radial circuit serving only single sockets higher than 32A ?

2 x 6mm would be the most a socket could take so probably 40A OCPD (singles in trunking).
With 9.3KW ,Ib=40.4a so In >=40a
It>=43a assuming ambient temperature is 35°c.
If you use reference method A (enclosed in conduit in an insulated wall) you are going to end up with a10mm cable which i think is expensive and difficult to terminate in a radial.
So i suggest you split the load into 2 radial circuits with Ib = 20a each wiring in 2.5mm.You can use 4mm as well with the same ref.method which is also expensive compared with the 2.5mm.
 
9.3kw

9.3KW

With 9.3KW ,Ib=40.4a so In >=40a
It>=43a assuming ambient temperature is 35°c.
If you use reference method A (enclosed in conduit in an insulated wall) you are going to end up with a10mm cable which i think is expensive and difficult to terminate in a radial.
So i suggest you split the load into 2 radial circuits with Ib = 20a each wiring in 2.5mm.You can use 4mm as well with the same ref.method which is also expensive compared with the 2.5mm.

Its singles in conduit run surface, 6mm singles can then handle 40A. Diversity of the appliances brings the Ib to less than 40A.
 

Reply to BS 1363 socket circuit in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

An example of the long term race to the bottom of quality of work in our industry, IMHO.
Replies
7
Views
585
  • Question
Thanks for the input guys. Lighting track is out of the question. The routing (h section guirders and angle iron) means that swa cable clipped...
Replies
12
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top