bill01803

-
Arms
Joined
Jan 8, 2012
Messages
483
Reaction score
400
Location
Devon
Hi all, I was asked in the office last night what size cable would be required for a 12V 1000W windlass with a cable length of 14m. I know how to calculate but where do you find the tables for 12V volt drop etc?
 
Hi,it is a pretty standard install. Use 50mm high quality welding cable,and get someone to sort the runs and containment,correctly.
Long runs of multi-stranded flexible,can be very hygroscopic,and will need correct attention,at terminations.

Make sure the installer understands the word "hygroscopic"....as the yankee spell-check,has failed :rolleyes:
 
Hi all, I was asked in the office last night what size cable would be required for a 12V 1000W windlass with a cable length of 14m. I know how to calculate but where do you find the tables for 12V volt drop etc?

It's the same volt drop table as any other voltage, the resistance of the cable doesn't change.
 
Other details,i forgot to add,were it's duty ratings. It's not a bow-thruster,so it will have short duty-cycles (all in the MI) and 1000W is the maximum,so majority of use will be way below,at no-load operation.

Anchor winch,would be a whole different basket of whelks...
 
Well,i suppose it's all relative....

It's forecast a change,to 10,and you need to do a rake of furling and unfurling,to get back to safe waters....

The cable,is an average length of site,MMA welding cable....

I wonder which job,is the one where you thought "Mmmm,i'm glad i spent that money..." :)
 
Just the job for me indeed...provided it's Capstan Full Strength!
However, just for clarification, is this an anchor windlass or a furler we're talking about? Clearly, the Lofrans linked to above is the former...
 

Reply to Cable selection on boat for 1000W motor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Once you have designed your switchgear layout, You could try, New Circuit engineering, Close Engineering or Blackburn Starling to manufacture for...
Replies
4
Views
513
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
574
Hi everyone, I'm looking to do some cable runs for cat6 etc in my house and was looking for some advice on blind wiring. I'm not skilled but I...
Replies
0
Views
975
For most domestic work the "standard circuits" in the On-Site Guide Table 7.1(ii) are all pre-checked for adequacy in these aspects, also there is...
Replies
3
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks