Circuit Breaker needed for Split Air-con with Inverter | Page 2 | on ElectriciansForums

Discuss Circuit Breaker needed for Split Air-con with Inverter in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 31, 2019
Messages
12
Reaction score
0
Location
Germany
Hello all. I´m installing a new multi split Air Conditioning (Inverter Type) in my dwelling and I have to purchase all of the electrical parts needed for the installer. I am currently running a 63a Type-A RCCB and I was told by the electrician that I could use the Type-A with a 16a Type-C MCB but according to my research, I need to upgrade to a Type-B RCCB. Does anyone have any experience in this?
 
FWIW, never had to install a Type B yet for these small units. The larger ones dont yet command RCD protection.... suspect that may change.......
The leakage currents are very very small and the more modern the unit the less impact they are having on supply harmonics. I would expect the latest Daikin baby unit to be more than happy on a type A.
UNLESS Daikin STATE IT MUST BE A TYPE B
 
Just a thought though. A/C units do leak to earth, even if its a small amount. I do remember one flat i went to that had 3 large units all fed off one up front RCCB, they were experiencing random tripping. Once i added all the leakage from the AV equipment they had as well as the a/c, there was no wonder it was tripping as the combined leakage of the whole flat was well above 15mA, cannot remember how far over it was but i simply put each a.c unit on a separte RCBO.....
 
Agree with C16 either MCB or RCBO depending on whats up front. This system looks like a 2 room multi-split with both rooms indoor units powered from a 3C+ earth direct to outdoor unit. I personally do not use indoor local isolation as there is little point, you still need to isolate the compressor before working on it. So i cable direct using YY cable. Daikin are the Daddy, R32 gas is the new stuff bit more flammable than R410A so have it serviced regularly.. .....
It's a 2 room multi 2.5kw for bedroom and 3.5kw for living room. I ran a 4x1.5 between both indoor units to outdoor. I ran all cable through cable canal and piping canals
Just a thought though. A/C units do leak to earth, even if its a small amount. I do remember one flat i went to that had 3 large units all fed off one up front RCCB, they were experiencing random tripping. Once i added all the leakage from the AV equipment they had as well as the a/c, there was no wonder it was tripping as the combined leakage of the whole flat was well above 15mA, cannot remember how far over it was but i simply put each a.c unit on a separte RCBO.....
Thanks for the reply. As I said before, I am no electrician. My father is, and I worked with him many of summers in his company but he´s in America and the US has a completely different system. I also wasn´t allowed to do any work in the breaker box and for good reason. With that said, I have a "decent" understanding of running wires, connections, GFCI´s, etc..I however don´t completely understand everything in the box. This is exactly what Daikin gives in the manual. It´s quite vague. Nowhere does it specificly state that it must be a Type-B but according to my research, it would need a Type-B because of the inverter. We also do have several computers if that does play a role.
[ElectriciansForums.net] Circuit Breaker needed for Split Air-con with Inverter
 
My electrician friend here said that he would recommend leaving the Type-A and just installing a C16 for the unit. Any thoughts? Or would I be better with a RCBO "x"16? Would the RCBO be run off of/in sequence with the RCCB or would that cause problems?
 
Last edited:
Valid options are: C16 MCB leave RCCB in place as electrician suggests, possible outcome too much leakage overall, however, this is a small chance. I have two outdoor units off a RCCB in Spain but there's just a TV, Sat receiver and laptop.
2nd option C16 RCBO, this will need the board to be re-jigged and may not be physically possible if the board is old and not designed for RCBO's. / not enough room for a common isolator if there is not one already.
I would go with your electricians suggestion as if it does not work, he will be the one to figure out why.
 
My electrician friend here said that he would recommend leaving the Type-A and just installing a C16 for the unit. Any thoughts? Or would I be better with a RCBO "x"16? Would the RCBO be run off of/in sequence with the RCCB or would that cause problems?

Where an upstream device is rated similar to the RCBO, there will be no selectivity therefore won't prevent nuisance tripping.
 
Valid options are: C16 MCB leave RCCB in place as electrician suggests, possible outcome too much leakage overall, however, this is a small chance. I have two outdoor units off a RCCB in Spain but there's just a TV, Sat receiver and laptop.
2nd option C16 RCBO, this will need the board to be re-jigged and may not be physically possible if the board is old and not designed for RCBO's. / not enough room for a common isolator if there is not one already.
I would go with your electricians suggestion as if it does not work, he will be the one to figure out why.
Thanks. I believe we will start there. In any case, we would still need to install the c16. We can always get a Type-B RCCB later and install if needed.
 

Reply to Circuit Breaker needed for Split Air-con with Inverter in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
I went out to a couple of the diy style AC units back in the day. One I remember the PCB was showing a fault code, the technical team had no idea...
2
Replies
23
Views
2K
Excellent. To be fair it was James who solved this one. Got to say I would sooner be in the garage watching the lathe than in the house watching...
Replies
11
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top