Morning all, nipped over from The tiling forum to run a question by you regarding electric ufh, so I'm happy to install the mat and run a continuity test before leveling over and laying tiles, a registered electrician is then usually sourced by my customers to connect up and sort the power out ...but my question is, is it ok for a 9sqm 200watt mat to be wired up to a spur nicked off a socket run or should it have its own feed direct from fuse box and whilst we're on the subject out of interest what would the maximum size 200w mat this is ok to do?

Note; I am not getting involved with messing with any electrics its just something ive witnessed recently and would like peace of mind for my customer it has been done correctly.. Thanks all..
 
200w/sqm = 1800 w
That load is ok to take off a fused spur as you describe..
But, what needs to be checked is that the socket circuit that you propose to spur off is actually ok..- correct size cable, fuse/mcb, RCD protection..
If everything is ok with that circuit then yes just spur out from an existing socket to a fused outlet
 
Last edited:
TBH it would be a worthwhile investment if you're doing this sort of installation quite often to invest in a cheap and basic tester to do some testing before you install the mat and once you've finished tiling.

This way you can confirm the mat works from the factory and was not damaged when you did the tiling.

All you would need then is your sparky mate to test, connect and certify as you're doing now comfortable in the knowledge that the UFH will work.

We know how expensive things can get when a UFH system doesn't work.

Something like this: Electrical Insulation Tester - Electrical Cable Insulation Test Meter - https://www.test-meter.co.uk/electrical-insulation-tester/
 
I have no electrical training or knowledge but ive got a multi meter, no idea what the different settings on it are for.. A sparky once put it on the right setting for testing resistance for me and that's where its stayed.. To be honest the numbers mean nothing to me. I just check the mat before laying it, after laying and and before I leave the job after tiling..
 
That’s ok for the functional side of the mat but for safety reasons the integrity of the wiring to earth needs to be checked too..
worst case scenario would be naked homeowner doing the moonwalk and tap dance across the bathroom floor :tearsofjoy:
 
Oh ok, never knew about that and I've fitted a lot of ufh..bit of a worry!! I take it that test should be done before instillation? Is that something this meter I have can check and if so how? [ElectriciansForums.net] UFH question for a tiler..
 

Reply to UFH question for a tiler.. in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Article
Rather than covering the issue, find where the moisture is coming from and address from that end, is the outside ground level above the inside, is...
Replies
1
Views
222
  • Question
Obviously not a building/DIY forum so will keep it short but yes - we've taken all the floors up. Several joists in the bathroom need doing as...
Replies
8
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top