Hi, I am new to this forum and can't find an exact match to my search.
I am new to testing and inspection and have come across a db mounted in a garage on the wall whereby the t and e's for all circuits are clipped direct to the wall before entering the ceiling approx 1m above.
Is this deemed as a C2 or C3 on test cert?

Thanks.
 
What do the regulations referenced in section 4.16 have to say about the example of wiring you are inspecting ?

Hi Andy. Thanks for your help on this. Really appreciated. I have re-read the sections in the regs and they refer to mechanical strain, not mechanical protection as I had read it earlier too hastily.
 
Last edited by a moderator:
The outer sheath is classed as mechanical protection. The environment the cables are installed in will dictate if it is sufficient mechanical protection. For example T&E clipped on a wall at high level with nothing around it would not warrant any code. T&E clipped just above a shelf used for heavy items may warrant a C2/3.

Thank you. I perceived the regs incorrectly.
 
might not warrant a code, unfortunately there isn't a code for an eyesore. it's R.A.F. ( Rough As F*CK)
 
On an older existing installs I am not overly fussed about clipped direct so long as it shows no evidence of damage.
I have clipped twin and earth in my garage from new been there for 30+ years and absolutely fine with this.
Same with older installs with non rcd on the lighting I am not overly concerned.
I have non rcd lighting.

Now if in the OP the cable sheathing was all chaffed and bashed up I would suggest so over capping
 
In the U.K. the outer pvc sheath is considered mechanical protection on twin and earth

Now in America and Canada the outer jacket is not classed as mechanical protection and if run on wall should be either in flexicon or ridged con-do-it or boxed in
 
Hi, I am new to this forum and can't find an exact match to my search.
I am new to testing and inspection and have come across a db mounted in a garage on the wall whereby the t and e's for all circuits are clipped direct to the wall before entering the ceiling approx 1m above.
Is this deemed as a C2 or C3 on test cert?

Thanks.
Have you done the actual course in testing???
Because if you had you would know .
According to your question you don' t seem to know what these codes mean.
 

Reply to Exposed T and E's during test. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
489
  • Question
Ha ha, I like the way the mole appeared right on cue in the right place. It might work in some soils, but around here it could go anywhere after...
Replies
17
Views
4K
  • Question
Couldn't agree more.
2
Replies
26
Views
3K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2
Replies
45
Views
5K
i would split he tails and fit an additional 2/3 way CU to supply the garage/whatever. that way you could feed in SWA, installung RCDs as and if...
Replies
3
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks