Was called out to a job to fix some damaged sockets for a landlord between tenants. Found this old Ashley & Rock CU.
Advised landlord that it is non-compliant, no RCD, mixed manufacturers etc. and that it should really be upgraded before he rents out again. Her response was that it's always been like that and there have not been any problems and I am only trying to create work for myself.
I have made the damaged socket safe (The original job).
As the property is for rental I am tempted to contact the council housing dept and report it, just wondering what the groups group's thoughts were.

[ElectriciansForums.net] Ashley & Rock CU no RCD
 
There’s no requirement in BS7671 for a CU to contain an RCD.
The prohibition on mixing different manufacturer’s devices has only come about because of the new standard introduced in amendment 3 of the 17th.
Prior to that, you could mix and match, as long as each component had a breaking capacity greater than the PFC.

Yes circuits of a location containing a bath or shower now require RCD protection, as do lighting circuits.

Yes the CU doesn’t comply with the latest edition of the Regulations.
However there is no requirement to upgrade to the latest edition, if the installation complied with the Regulations at the time of design.
 
As far as rental properties go , that consumers unit if one of the better ones you are likely to see....
Nearly every one I see has massive holes in the front from missing blanks.
 
You're joking aren't you ?
what legislation will you be quoting that requires RCDs to be fitted in rented accommodation ?
Best give Hager a call too as they will confirm that those breakers are a direct match and they have no problem with their current range being used with that CU.
 
I do love a bit of baiting
The issue of the mixed mcb’s is interesting, I’ll have to call Hager on Monday to confirm that.
Wouldn’t bother with the council as it is not worth the hassle and was probably a bit of a knee jerk comment. To add fuel to the fire,I did find this on New tougher electrical safety standards to protect private tenants - https://www.gov.uk/government/news/new-tougher-electrical-safety-standards-to-protect-private-tenants

There are existing regulatory requirements to help protect tenants:

  • mandatory 5 yearly electrical installation checks for Houses in Multiple Occupation (HMOs)

  • the Landlord and Tenant Act 1985 requires landlords to keep installations in the property, including the supply of electricity, in good repair and proper working order

  • building regulations since 2010 have required all circuits in new or rewired homes to comply with the wiring rules in BS 7671 and include the installation of a Residual Current Device (RCD) covering any new circuits in the consumer unit since July 2008

  • local authorities have powers, through the Housing Act 2004, to take action where there are electrical hazards in a property
 
A landlord is legally obliged to ensure the property is electrically safe and it is only HMOs where a Periodic Inspection is stipulated. The lack of additional rcd protection does not necessarily imply it is not safe.
 

Reply to Ashley & Rock CU no RCD in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top