I have come across a fault that I am struggling to find. I cant remember being stumped like this before as I like fault finding and have always found the fault before.

6A MCB is tripping on lights. It sometimes trips the moment it is switched on and sometimes takes up to 30 mins. There is no RCD.

IR readings are poor (o.3Mohms L/N - E) but do not show a short circuit to earth. I have removed all lamps but IR readings for L-N still suggests something is on the circuit which I cannot find (0.05Mohms).

I have tried it on another 6A MCB, it trips, so not a faulty MCB.

It will not be an over current as there is little on the circuit (2 bathroom lights, 1 x kitchen, utility, garage, perhaps 2A absolute max).

My plan is now to break the circuit in half and leave. Customer can tell me if it trips or not. I can carry on like that but it means many trips and they are not close.

I could also try it on the RCD side to see if it trips the RCD (meaning a L-E fault, but would this knowledge help?)

Any suggestions?
 
whack 1000v across LN-E.....NOT L-N (!)
This is a good trick. Even if the fault doesn't avalanche, it can at least give a significantly different reading that indicates something unstable. Testing at 250V can give a similar indication by way of a much higher reading.

Here, I have a choice of insulation testers. 250V, 500V, 1kV, 2.5kV, 15kV and Cuthbert. In Cuthbert v. domestic wiring, if there are no faults, Cuthbert will create some for you. 60kV at enough current to carbonise you. He's really for testing HV lines.
 
No. If there is rodent damage to a cable, for example, there might be all manner of simultaneous problems. In fact, the 0.05MΩ might be one of them. The tripping might be flashovers L-N hence won't take out the RCD, but the 0.3MΩ is where the bared length of L is resting against brickwork so won't go low enough to trip the RCD either.

No evidence is irrelevant until the case is closed.
I did forget to mention something! :oops:
A mouse has been recently seen in the property:oops::oops::oops:
 
I have quizzed the customer quite a bit.
No new work.
No trades in recently.
No DIY work.
They did not initially switch something on for it to trip, it just tripped.

You have simply forgotten golden rules 1 & 2

Golden Rule No 1 = Customers Lie
Golden Rule No 2 = Refer to rule number 1

See my recent post in The Arms, everything now is rodent damage!
 
I sometimes whack 1000v across LN-E.....NOT L-N (!). It is often enough to break down an intermittent fault into a dead short, which is easier to locate.

This is a good trick. Even if the fault doesn't avalanche, it can at least give a significantly different reading that indicates something unstable. Testing at 250V can give a similar indication by way of a much higher reading.

Here, I have a choice of insulation testers. 250V, 500V, 1kV, 2.5kV, 15kV and Cuthbert. In Cuthbert v. domestic wiring, if there are no faults, Cuthbert will create some for you. 60kV at enough current to carbonise you. He's really for testing HV lines.

Thanks for this.
Would you say that testing at varying voltage gives varying results ...
always, usually, sometimes, rarely? I mean this with regards a fault, not when testing a healthy circuit (as the results will be similar).
It's just useful to know how much credence to give to the results hence the options above.
 
I have come across a fault that I am struggling to find. I cant remember being stumped like this before as I like fault finding and have always found the fault before.

6A MCB is tripping on lights. It sometimes trips the moment it is switched on and sometimes takes up to 30 mins. There is no RCD.

IR readings are poor (o.3Mohms L/N - E) but do not show a short circuit to earth. I have removed all lamps but IR readings for L-N still suggests something is on the circuit which I cannot find (0.05Mohms).

I have tried it on another 6A MCB, it trips, so not a faulty MCB.

It will not be an over current as there is little on the circuit (2 bathroom lights, 1 x kitchen, utility, garage, perhaps 2A absolute max).

My plan is now to break the circuit in half and leave. Customer can tell me if it trips or not. I can carry on like that but it means many trips and they are not close.

I could also try it on the RCD side to see if it trips the RCD (meaning a L-E fault, but would this knowledge help?)

Any suggestions?
Find the fault that is giving you 0.05Mohms. halving the circuit and asking the customer to let you know if it trips does not come over very well apologise for being blunt but there it is.
 
I did forget to mention something! :oops:
A mouse has been recently seen in the property:oops::oops::oops:
Perhaps I should take my fairly newly acquired air rifle instead of my MFT!
I bought an air rifle to shoot a squirrel in the loft that was giving me sleepless nights.
I had moved my bed downstairs it was so bad.
It would go against my beliefs to just kill it without making use of it so I had read up on how to skin it and cook it.
I practised with the rifle for a couple of weeks so that I would be a good shot and not merely injure the animal.
I heard it one night.
I went up with my head torch and rifle.... into the loft.
I saw it right in the corner!
I took aim......
I continued to take aim.....
I remained continuing to take aim.....
for around 2 minutes....
It ran away!

It left soon after and I moved back into my bedroom :).
I realise this story is a bit odd, but it is true.
 
Perhaps I should take my fairly newly acquired air rifle instead of my MFT!
I bought an air rifle to shoot a squirrel in the loft that was giving me sleepless nights.
I had moved my bed downstairs it was so bad.
It would go against my beliefs to just kill it without making use of it so I had read up on how to skin it and cook it.
I practised with the rifle for a couple of weeks so that I would be a good shot and not merely injure the animal.
I heard it one night.
I went up with my head torch and rifle.... into the loft.
I saw it right in the corner!
I took aim......
I continued to take aim.....
I remained continuing to take aim.....
for around 2 minutes....
It ran away!

It left soon after and I moved back into my bedroom :).
I realise this story is a bit odd, but it is true.

You bought an air rifle to shoot an animal even though this was against your beliefs ? Surely a humane trap would have been a smarter buy ?

Good to know that threatening it worked well enough anyway :D
 
Find the fault that is giving you 0.05Mohms. halving the circuit and asking the customer to let you know if it trips does not come over very well apologise for being blunt but there it is.
I agree Anthony.
I'm going to go down there tomorrow and find it!
Thanks for reminding me of my moral duty and I shall update you all.
 
You bought an air rifle to shoot an animal even though this was against your beliefs ? Surely a humane trap would have been a smarter buy ?

Good to know that threatening it worked well enough anyway :D
T
Is the lighting circuit wired as loop in or neutrals at switches?

With so few lights narrowing it down to a section shouldn’t be too tricky.

Had this recently and mice were to blame .....
Neutrals are in the light fittings.
 
Neutrals are in the light fittings.

I’d slowly taking it apart .... another one from the mists of time was where the switch drop cable had been trapped and damaged where boards had been laid in the loft, and the board pinched the cable as it entered the metal conduit .....

You will be really chuffed when you solve this

The necessary ingredients are patience, paper, pencil or pen and your test kit .. and a customer knowing that the bill will only be known when it’s done and dusted
 
don't let the IR test mislead, remember it would only be accurate for a linear resistance. The MCB will trip on reactive power as well as real power but with DC IR testing you'll only notice what would transfer the real power.
Could be a faulty PSU somewhere causing the issue perhaps.
Or it could be the mouse!
Can you get a clamp meter on the circuit when the MCB is on?
 
I may have to do that, but I was hoping to track it down with fault finding/testing rather than undoing everything on the circuit.

There are only so many tests you can do before you have to undo something and test again this may need to be repeated a number of times until you find the fault
If the fault is big enough to allow a circuit tracer to function you can sometimes use this to take you to the fault without having to break the circuit down
 
don't let the IR test mislead, remember it would only be accurate for a linear resistance. The MCB will trip on reactive power as well as real power but with DC IR testing you'll only notice what would transfer the real power.
Could be a faulty PSU somewhere causing the issue perhaps.
Or it could be the mouse!
Can you get a clamp meter on the circuit when the MCB is on?
Yes I could, but would this not just show the 1 or 2 A running through it at that time? It may change rapidly when it's about to trip but I don't think I can get away with standing there for 30 mins :)
Anyway, I am now leaving to find it!
 
Last edited:
found the fault?
Just found it!
L/N -E results were now 0.03Meg. Traced the fault to between 2 lighting points.
Unfortunately this was between the main house and flat roofed extension.
Traced the cable in the loft where is disappeared into the cavity between main house and extension.
Crawled to edge as far as I could and poked the inspection camera down into the cavity.
This is what I saw..
[ElectriciansForums.net] Difficult fault to find? [ElectriciansForums.net] Difficult fault to find? [ElectriciansForums.net] Difficult fault to find?
Sorry for poor quality but this is me taking a picture with my phone of what the inspection camera was seeing.
Looks like the naughty mouse!
Ps.. looks like he's started on the socket cable nearby as well which you can just make out in one if the pics.
 
Last edited:
Just found it!
L/N -E results were now 0.03Meg. Traced the fault to between 2 lighting points.
Unfortunately this was between the main house and flat roofed extension.
Traced the cable in the loft where is disappeared into the cavity between main house and extension.
Crawled to edge as far as I could and poked the inspection camera down into the cavity.
This is what I saw..
View attachment 49768 View attachment 49769 View attachment 49770
Sorry for poor quality but this is me taking a picture with my phone of what the inspection camera was seeing.
Looks like the naughty mouse!

congratulations.
bet you feel better already.
 

Reply to Difficult fault to find? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
696
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
557
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...
Replies
0
Views
357
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
445
davesparks
D
  • Question
has anybody tested the coffee machine for safety? I would try putting a normal load on the same supply as the monitor and see if that goes off at...
Replies
9
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks