Testing with a CU change | Page 2 | on ElectriciansForums

Discuss Testing with a CU change in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 13, 2016
Messages
592
Reaction score
51
Location
London
Working with a spark, now when we change a CU no new circuits just old for new, We do all end to ends on rings, IR tests and Zs making sure all the new protective devices that disconnection times are met, would you do R1+R2?

If we do a CU change and add new circuits we do R1+R2 on the new circuits what do you guys do?
 
I thought zs=Ze+ (R1+R2)...but Ze does not = Zs-(R1+R2) or something like that possibly maybe......I’m feeling really uncomfortable with the new look.....the only other time I’ve felt like this was when they spruced up my local! Took me ages to get over that....
You can not do R1 +R2 = Zs -Ze as for the parallel paths
 
You can not do R1 +R2 = Zs -Ze as for the parallel paths

If we are talking domestic, mostly twin and earth cabling

You can calculate this fairly accurately, if your in any doubt, if you take your ZS then remove your ze, then have an approximate idea of cable run you can look at the resisstance per meter


Rings are easier to confirm with the exception of a long spur from the furthest point

i only usually find parallell paths in a domestic setting on immersion circuits/ring circuits with heating/boilers etc on and houses with supp bonding

Commercial/ind jobs using a lot of metal work are of course
another matter

Obviously r1 and r2 on TT systems domestic or otherwise i would measure in all circumstances
 
Calm down

[ElectriciansForums.net] Testing with a CU change
 
It definitely doesn't feel write to determine R1+R2 by subtracting Ze from Zs.
From a mathematical point of view it works just fine and is 100% correct with respect to rearranging the equation Zs = Ze + (R1+R2), but your Zs is influenced by other earthing paths that your Ze is not influenced by so you could get a biased answer.

Although... that would be true of the initial equation as well! Ze could be 100Ω on a TT. Zs could be much lower than that if the bonding conductors have a good pathway to earth, ∴ in this case Zs ≠ Ze + (R1+R2).

I enjoyed all those mathematical symbols, it's been a while! I miss good old fashioned maths where the answer is black and white.
 
#
Sorry the wrong way around ZS = ZE (R1+R2) must leave the red alone sorry Ant you are right my apologies.
That is also wrong Pete. Ze(R1+R2) means Ze x (R1+R2). Pedantic I know but I like maths to be correctly written, not too worried about englush!
 
I am also not a fan of determining R1+R2 using Zs.
It’s useful, yes but also misleading..
IMO R1+R2 is to determine the resistance of the respective cables. Furthermore, if the length of the circuits needed to be verified then using Zs - Ze would give incorrect values.
 
I thought zs=Ze+ (R1+R2)...but Ze does not = Zs-(R1+R2) or something like that possibly maybe......I’m feeling really uncomfortable with the new look.....the only other time I’ve felt like this was when they spruced up my local! Took me ages to get over that....
they done same with my local back in the 90's. knocked down walls, stables, ripped out woodworm infested bar and all the grime. refurbished into a food orientated, child friendly, monstrosity. what used to be nice friendly pub where I got barred on the Friday and reinstated on the Monday ( massive drop in takings) then became a plastic copy of what a pub might be.
 
How do you calculate your R1+R2 as that should only be done by measurement only other than at the design stage?
Agree But you also don't calculate R1+R2 and design stage either , you calculate Zs from by inquiring what the Ze will be and adding that your R1+ R2 readings, As others have said you can't back calculate the R1+R2 but I believe loads sparks who do it, As for the ops question, I do all the test except Zs which I calculate .
 

Reply to Testing with a CU change in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

I have a question i hope someone can just give me a little clarification on . When carrying out preliminary cable design for a given circuit we...
Replies
0
Views
216
  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top