Hi guys and girls,

Changed over my first CU today (didn't go bang so I'm classing it a success), with regards to the EIC do I list every circuit and fill it in as if they were new circuits, I've had a look at the best practice guide for CU's and the way i'm reading it it would suggest yes as its the schedule of test results but wasn't sure if i'm going overboard? I've got all the values from all the pre and post tests so easy enough to do but wanted to check i'm doing it right and if there is anything else I need to add in the comments for a CU change? Ps.. was just the CU being changed no physical alterations to any of the circuits
 
According to BS7671 the Certificate is not valid without the schedule/s. Best place to look not best practice guides.

Yes I didn't mean whether to attach the schedule of test results I meant about listing every circuit or if there was something specific to do for a CU change, having not seen anything otherwise my instinct would be to do it as if they are all new circuits but wanted to ask some of the experienced sparks on here as they have been very helpful on some other things i've asked.
 
When you change a CU, you are altering ALL the OCPDs and therefore your inspection and testing needs to confirm that the new devices are suitable for use there after ...

Tedious, yes, necessary, absolutely

And if you are in England or Wales the new CU requires part p notification too
 
When you change a CU, you are altering ALL the OCPDs and therefore your inspection and testing needs to confirm that the new devices are suitable for use there after ...

Tedious, yes, necessary, absolutely

And if you are in England or Wales the new CU requires part p notification too

Hi Murdoch, yes done all the testing before and after the change, happy with all that it was just the actual filling in on the EIC, want to check that listing each circuit on the schedule of tests as if they were new curcuits is the correct thing to do
 
The requirement is to test and record the results of any existing circuit that has been altered or new circuit that has been installed.
Note 1 for EICs prohibits the use of an EIC to report on the condition of an existing installation.

Some will say that you’ve changed the characteristics of each circuit, so in effect altered them.
To a certain extent, that’s true, however it is only a problem when changing rewire-able or cartridge fuses to MCB/RCBOs with a rating below 15A/16A.
All B type BS EN 60898 MCBs and BS EN 61009 RCBOs 16A and above have a higher maximum permitted Zs than the corresponding rewire-able or cartridge fuse.

As such you would need to verify the Zs on any 6A or 10A B type MCB/RCBOs and of course for any C or D type if installed.

As for the rest, it’s entirely up to you.
A complete schedule is useful for further reference when periodic inspection are conducted, and also a copy of the schedule can be placed in or near the board to identify circuits.

You do need to make sure that under ‘extent of installation covered by this Certificate’, you make it quite clear what work is covered.
 
please explain on that score .

Prior to the change I tested the main bonding continuity, the ze, continuity of r1r2's of the circuits, and IR tests of the circuits but Line and nuetral connected to earth and Zs and then post change did the Zs again where there were sockets and RCD tests pefc,pscc,polarity did everything as if it was a complete new install basically
 
Sounds like you have gone about it the correct way. Test first always a good rule of thumb.
Thanks thats good to hear I'd rather start off as I mean to go on in a sense and do things the right way, that said can always learn more stuff so thats why I think this forum is great, so from what i've read then il fill out the EIC as I would for a new install with all the circuits on the schedule of tests sheet, thanks guys
 
Thanks thats good to hear I'd rather start off as I mean to go on in a sense and do things the right way, that said can always learn more stuff so thats why I think this forum is great, so from what i've read then il fill out the EIC as I would for a new install with all the circuits on the schedule of tests sheet
[ElectriciansForums.net] EIC Consumer unit change
 

Reply to EIC Consumer unit change in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

M
  • Question
I meant EIC, No idea why I put EICR down, thanks for the clarification
Replies
13
Views
1K

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top