Giving a hand to some sparks on a real nice job..but..
Anyone fitted the power track system,bus bar & the plug off’s to sockets.
It states they are 3 metre lengths,if over then these leads need to be fused.
It’s a 63 amp system,with a 40 amp Rcd,also plug in 1.5mm flex,can’t get my head around this.
It’s all factory made,& all the bits have been sent,but why a 40 amp Rcd protecting the cable.
So it’s 63 amps,leads are 4.0mm straight from plug off,then 1.5mm of the Rcd.
 
I think the power track we installed had a 32A protective device feeding the track and the floor boxes had 4mm from the box to the plugin installed inmetallic flexible conduit.
 
This is the sort of equipment,this plugs straight into the 63 amp bus bar system.
 

Attachments

  • [ElectriciansForums.net] Power track in offices
    9A16E689-3A7C-467F-9D98-9A073C150EC1.jpeg
    524.3 KB · Views: 25

Reply to Power track in offices in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

  • Question
Leaves the potential nuisance of knocking off a raft of equipment unnecessarily
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top