Hi

Just carried out a PIR and the cut out has been completely covered/boarded over - how do I go about recording Protective Device information? what code if any can I give this?

Also can anyone hazard a guess at the age of the installation from the photos please?

Thanks

P.S.

Forgot to ask - this is my first commercial PIR do the same rules apply to bonding (there is none) and RCD protection for socket outlets (again there is none) as it does to domestic.

Mark
 

Attachments

  • [ElectriciansForums.net] Distributors Cut Out (Or lack of)
    Cut Out.jpg
    139.2 KB · Views: 46
  • [ElectriciansForums.net] Distributors Cut Out (Or lack of)
    DSCN2692.jpg
    186.5 KB · Views: 43
  • [ElectriciansForums.net] Distributors Cut Out (Or lack of)
    DSCN2695.jpg
    243.4 KB · Views: 43
  • [ElectriciansForums.net] Distributors Cut Out (Or lack of)
    DSCN2696.jpg
    242.6 KB · Views: 42
  • [ElectriciansForums.net] Distributors Cut Out (Or lack of)
    DSCN2691.jpg
    139.4 KB · Views: 42
Last edited:
Just carried out a PIR and the cut out has been completely covered/boarded over - how do I go about recording Protective Device information? what code if any can I give this?

LIM the characteristics of the OPD And CODE 3 the Observation on page 2 and refer to the photos

Also can anyone hazard a guess at the age of the installation from the photos please?

>35 years - Evidence of alterations = YES - Estimated Age <5 years

Forgot to ask - this is my first commercial PIR do the same rules apply to bonding (there is none) and RCD protection for socket outlets (again there is none) as it does to domestic.

YES - same rules apply
But do the sockets outlets need additional protection?
 
Hi Semaphore

Thanks for the helpful advice - Socket outlets in the office are behind plasterboard partition with T&E less than 50mm so I would assume protection required.

Socket outlets in workshop are singles run in metal conduit but are used with extension lead to operate appliances (inspection lamps etc) outdoors - would these require protection?


Thanks

Mark
 
yes mate,
additional protection by 30mA rcd must be provided for socket outlets supplying mobile equipment with a current rating not exceeding 32 A for use outdoors
and also for the sockets in the office installed at a depth of less than 50mm

just re wrote it mate
 
Last edited:
Newpark7

It's a yes to both then
And probably the Portable Appliances need testing too?
And possibly additional sockets installed to prevent extension leads from being used?
Are they a trip hazard?
 

Reply to Distributors Cut Out (Or lack of) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar threads

Thanks all for your comments, advice and suggestions. The following is probably pretty boring for most, and is simply a summary of how the job...
Replies
8
Views
676

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top