I'll make this as short as possible.

This is what I have:

1) Inverter: Aukey 1000 W
2) Solar Controller: 40A
3) Battery: Solar battery 100 Ah C100
4) Solar Panels: One 100W PET Panel

I want to follow this:

[ElectriciansForums.net] Need help with fuse


My Question:

What Amp fuse do I need to/from everywhere? (Yes, I'm a noob, this is my first project)

The fuse go to a fuse holder then connection right?

Can I use a circuit breaker instead of fuse?

Update: Sorry forgot to add 12V
 
Last edited:
12 AWG is usually rated at 20A.
Though a 100W panel at 12V will produce just over 8A.
So anywhere between 8.5A and 20A should be fine.

4AWG is usually rated at 70A.
However the Solar controller is rated at 40A.
So anywhere between 40A and 70A should be fine.

Make sure you also use 4AWG for the negative side between the battery and the inverter.
 
12 AWG is usually rated at 20A.
Though a 100W panel at 12V will produce just over 8A.
So anywhere between 8.5A and 20A should be fine.

4AWG is usually rated at 70A.
However the Solar controller is rated at 40A.
So anywhere between 40A and 70A should be fine.

Make sure you also use 4AWG for the negative side between the battery and the inverter.
Thank you so much!
 
spin is correct in saying the controller is 40A. however, with a fully charged battery and the inverter supplying it's full load capacity of 1000watts, that's 83 A @ 12V,
 

Reply to Need help with fuse in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

If the batteries are charged and the house is taking little then the full production of the panels will be dumped into the grid. As you have set...
Replies
1
Views
481
Need to crack on to get most from this year :cool: BTW if you are thinking about adding to the strings later, i.e. add more panels to existing...
Replies
6
Views
774
I would expect it to be virtually impossible to complete the project safely. how would you fix the panels to a roof that you can’t disturb? when...
Replies
1
Views
815
Just for the sake of completeness, here is the recently slightly updated OFGEM guidance. See the section "Changes to your installation": Feed-in...
Replies
10
Views
4K
The amount of power you can feed to the POCO is limited by YOUR POCO not the NEC or another governing body. Call the POCO and ask them...
Replies
1
Views
970

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks