RCD tripping under high load on 2 circuits | on ElectriciansForums

Discuss RCD tripping under high load on 2 circuits in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jul 20, 2019
Messages
3
Reaction score
3
Location
Leicestershire
I’m in desperate need of someone with great fault finding knowledge. I have a dual rcd consumer unit as seen in picture. The left hand side rcd trips when anything with a high output like a tv for example is turned on in any sockets protected by the left rcd. The left rcd also trips when trying to switch on any light switches also protected by this rcd. The left rcd also trips if I use an appliance in the kitchen which is protected by the right hand side rcd, the appliances still work in the kitchen but they trip the left rcd and the rcd will not reset until I turn off whatever I’m using in the kitchen. I have had an electrician come round to investigate who left still scratching his head and told me that a full test would need to be carried out on the consumer unit as the faults were not pointing to one specific thing as 2 circuits are tripping the left rcd and not just 1. My house is 4 years old and I have owned it since new, one problem I have had since owning the house is the bath leaks onto the living room ceiling. I’ve had the builders out twice for this but that problem still persists. It has been like it for 4 years so I’m not sure if it has finally caused a problem? To summarise, any high output appliance used in the sockets protected by the left rcd trips the left rcd and also the light switches protected by the left rcd trip the left rcd. Everything in the kitchen works but using them causes the left hand rcd to trip. I have switched the rcd units with each other to eliminate the possibility of an over sensitive rcd but it made no difference so I have now swapped them back. I have checked the wiring on the sockets and light switches protected by the left rcd but couldn’t see any damage/loose connections. Any advice would be greatly appreciated as I’ve been trying to diagnose this problem for a week without any proper testing equipment. Kind regards, Simon
[ElectriciansForums.net] RCD tripping under high load on 2 circuits
[ElectriciansForums.net] RCD tripping under high load on 2 circuits
[ElectriciansForums.net] RCD tripping under high load on 2 circuits
 
Last edited:
Get another electrician is my opinion.

With it being only on the left side you must have a minor fault on the left side circuits which is only becoming an issue when you are under a higher load. Any decent electrician should be able to split the circuits up and find the fault. It may be two very small faults that when together and connected through the neutrals are creating a bigger fault on any kind of load.

I've had this before and turned out to be a small fault on a dishwasher not the circuits itself.


I take it the electrician used a multimeter to test the circuits
 
Get another electrician is my opinion.

With it being only on the left side you must have a minor fault on the left side circuits which is only becoming an issue when you are under a higher load. Any decent electrician should be able to split the circuits up and find the fault. It may be two very small faults that when together and connected through the neutrals are creating a bigger fault on any kind of load.

I've had this before and turned out to be a small fault on a dishwasher not the circuits itself.


I take it the electrician used a multimeter to test the circuits
Thank you for your reply. The electrician who came round was actually a friend who I think thought it was going to be easier to diagnose than what it seems. He didn’t have any equipment with him but instead of waiting on help of friends I have another electrician coming round early next week to hopefully diagnose. Just wondered if anyone else has come across anything like this before, it’s interesting to read about your similar past fault tho.
 
Because a certain level of imbalance or leakage is required for a Rcd to operate,occasionally a neutral-earth fault on a lighting circuit will have insufficient current flow to cause that Rcd to operate
Sometimes when a heavy load is then used the current flow through that fault path then becomes high enough to operate the Rcd,the fault may not be with the load just used it could be via the lights or elsewhere but the symptoms can sometimes cause confusion
Needless to say ,the only sure way of determining whats at fault is by the use of test meters
 
RCD's are very finiky devices,
they won't tolerate any inter connection between the neutrals and the earth lines on the load side of the RCD.
so go thru all your circuits and make sure all neutral lines are keep completely independant of the earth lines.
 
One of the last jobs I did, was a CU replacement, kitchen & bathroom refurb. After I’d finished, I was called back a few weeks later to fit the bathroom vanity mirror.

Met by the kitchen fitters, who said there was no power upstairs. RCD had tripped. Quick look round, and spy a new socket on the landing, where the fitters had plugged in their hoover. Removed faceplate, and found neutrals pinched by faceplate screws.

Apparently, the client got a ‘mate’ in, and installed the landing socket. Obviously not tested.

Had anything like that OP?

PS, if the house is relatively new, do you have the original electrical installation certificate?
 
Last edited:
what he said ^^^, should not be hard to find if its tripping consistently. Half hour with a tester, 2 hours weeks without... lol
corrected that for you.
 
Classic symptoms of a typical N-E fault, usually on a circuit on the RCD that is tripping. But the loads that trigger it need not be on the same circuit, or even the same RCD, as any load on the CU will cause voltage drop on the supply side.

So, one circuit on the left RCD almost certainly has an N-E fault. Testing required to find which. Bear in mind it can also be something plugged into a socket, so try unplugging everything from the left RCD's sockets. However if very light loads such as individual lights trip it, the fault is more likely to be on that circuit. BTW the TV is not a heavy load, 100 watts or so unless its over 40 years old.
 
Last edited:
@Simonw586 Looking at the first picture it looks like there is no neutral on the outgoing side of the right hand RCD. The neutral going to the right hand neutral bar appears to be coming from the main switch and not the outgoing side of the right hand RCD. Can you check that out and confirm?
 
Looking at the first picture it looks like there is no neutral on the outgoing side of the right hand RCD. The neutral going to the right hand neutral bar appears to be coming from the main switch and not the outgoing side of the right hand RCD. Can you check that out and confirm?
Eagle eyes Sinatra :) .
 

Attachments

  • [ElectriciansForums.net] RCD tripping under high load on 2 circuits
    CA0CCBA5-8834-43F2-BA53-36CFC5F0E7EA.jpeg
    1.4 MB · Views: 37

Reply to RCD tripping under high load on 2 circuits in the UK Electrical Forum area at ElectriciansForums.net

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
610
davesparks
D
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
295

Recommended Sponsor News

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top