Been called to a job for a second opinion,
Previous spark said current db set up would warrant a code 2 and therefore need a board change.
Granted the elcb set up isn't great for discrimination but cant see this warranting more than a C3.
But what about the elcb itself?
It Tests out fine.
Any written confirmation that elcbs aren't compliant?
 

Attachments

  • [ElectriciansForums.net] 4293 elcb coding __________
    20190726_113809.jpg
    3.6 MB · Views: 38
Yes it is actually an rcd just realised, first spark must be after a Payday.
Thanks
came across a couple of these MEM RCDs. they totally ballsed up Zs readings. one was even to the extent of adding 349 ohms to the value.
 

Reply to 4293 elcb coding __________ in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

In the 80's I was taught that with PME earthing arrangements we used 16mm for the main earthing conductor, some went a bit crazy and were bonding...
Replies
11
Views
1K
D
We're booking in an out of hours visit for a full shutdown to fix some serious nasties and I'll sort this out while I'm there. I'm not doing an...
Replies
3
Views
1K
davesparks
D
Measuring earth leakage is not relevant, that is only relevant to actual unwanted tripping, we are not concerned with that, we are concerned with...
Replies
42
Views
5K
davesparks
D
With TN systems neutral is deemed to be at earth potential with TT it is not, so if the isolator only disconnects the lines there a possibility of...
Replies
6
Views
2K
C3 and c3 if no rcd, as the inspectoratei
Replies
18
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks