Hi, I'm not an electrician but a keen amateur. I understand the testing on RFC and how it's done but couldn't get my head round the (r1+r2)/4 calculation. I've trawled this site (and others) and it seems to me that a lot of people struggle to explain this fully. The truth is that this equation only holds up when the CSA of the conductors are equal - which is not the case with the line and cpc. I attach a document that I think explains it reasonably but I'm sure more experienced professionals can comment (which would be appreciated)
 

Attachments

  • final_divide_by_four.pdf
    33.5 KB · Views: 50
I do enjoy my Saturdays lol.
r1+r2 is halved cause its half the length (agreement on that), then the formula needs another division of 2 to satisfy (division of 4). So in that case its half the remainder
 
I do enjoy my Saturdays lol.
r1+r2 is halved cause its half the length (agreement on that), then the formula needs another division of 2 to satisfy (division of 4). So in that case its half the remainder
Yes, which will give us the R1 + R2.
The second halving is required because we have two conductors in parallel which reduces the resistance by half.
 
I wrote a Matlab script a while ago to determine the deviation from equality between R1+R2, and r1+r2/4, when the cpc and line conductors are different sizes.

For the different sizes of T&E available, the maximum discrepancy at the very edges of the ring was 20% (with 4+1.5mm cable); for 2.5+1.5mm, the maximum discrepancy was about 6%. If you've got old 2.5+1mm, you might get as much as 18%.

[ElectriciansForums.net] (r1+r2)/4, the myth expelled?


For all practical purposes, it's as near as Phuket is to swearing.
 

Reply to (r1+r2)/4, the myth expelled? in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top