[ElectriciansForums.net] Is this acceptable?
So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
 
The pfcc and pscc on a circuit run in 1 mm is going to be a lot lower than is required to break the incoming.
So no 1 mm won’t do it.

Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.
 
Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.

It's within a control panel, it's very common to see this and also panel lights, maintenance sockets and BMS supplies fed off the incoming side of the panel isolator. All marked, live when panel isolator is off.
 
The pfcc and pscc on a circuit run in 1 mm is going to be a lot lower than is required to break the incoming.
So no 1 mm won’t do it.

Edit : having read robs post. If there is a very low chance of a fault occurring then yes I may agree with him, but it’s not something I’d do.

It's a common method of doing things in control wiring.

However the stipulation is the wire length (<3m) and it hasn't to be likely damaged, so realistically, inside trunking within a control panel it's not.
 
View attachment 51295
So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
View attachment 51295
So the incoming power is coming from X1 and three phase is being distributed to Q1 using 25mm cable. Phase 1 & Neutral are going to Q2. I was curious as to what cable size is acceptable going to Q2? I assumed it would also need to be 25mm but I've been told as its pulling a maximum of 1A that 1mm is acceptable.
Is this correct or is this a safety hazard?
Thanks in advance, first time post and new to the industry.
The apprentice from what I’m seeing is the arrow you drew was pointing at the grounding conductor and after 30 amps you can defrayed the equipment ground. Looks fine to me
 
Although it is fine to do that as discussed above.
I prefer to size cable in that scenario bigger than required.
I think I would have used 4mm, apart from any other reason, it tends to fit the larger terminals found in the isolator a bit better.
 

Reply to Is this acceptable? in the Talk Electrician area at ElectriciansForums.net

Similar Threads

I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
574
I was doing remedials from another contractors EICR, they had recommended that the 315A fuses feeding the powelocks be changed for 200A due to the...
Replies
15
Views
3K
davesparks
D
  • Question
Ah, that may be different, but most keep to the same connection standard irrespective of single consumer, or multi-occupancy
Replies
22
Views
4K
For a 125 amp service I always pull 3 #4 copper and a # 8 ground. I know that copper is more expensive but it will slide in a 2 inch conduit very...
Replies
1
Views
940
  • Question
When sizing cables and circuit breakers the much simplified rule is: The cables maximum current carrying capacity must be greater than the...
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks