How to wire motor plug | Page 4 | on ElectriciansForums

Discuss How to wire motor plug in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

For the OP: what I have written below is for my electrical colleagues on the EF. You need someone to rewire afresh the whole machine which at the moment is an unsafe lash-up.

I have been studying the images the OP provided and have an alternative view on what has been wired.

Some assumptions:

1. The work lamp is 220Vac.

2. The motor is a three phase squirrel cage motor which can be wired 380V star or 220V delta.

3. The original manufacturer's wiring was for 3 phase operation at 380V and the TPDT centre off rotary switch enables Reverse - Off - Forward rotation of the motor - there are clues to this if you study the rotary switch images, the classic positions of the 4 solid links and the chopped of blue and green wires. The motor was wired as star.

4. I reckon (cannot be certain) but the original machine lead was 3 wire and earth. The lamp obtained its 220V ( = 380/1.713) by connecting across a line and the virtual neutral at the start point of the motor. If the lead was 4 wire and earth then an external neutral is provided which the lamp can use.

5. On one of the specification plate images it says the machine is for 380V, but at the bottom right 'Voltage - 220V needs to be customized and pay extra...'

I think then that the original 380V 3 phase star motor has been 'customized' to run on 220V single phase. The ability to swap motor direction has been disconnected and all the rotary switch does now is switch on/off the L and N to the motor. What the black wires does at the rotary switch I do not know without seeing what happens where it is sleeved with white sleeving - is it attached to the metalwork to be the cpc? For China this would be the wrong colour for the cpc - they use green/yellow - black or blue are reserved for the neutral.

To operate at 220V the motor must be wired as delta. The 'customization' is to attach the black plastic box over the original motor terminal housing and place a capacitor to the left and right as shown. These capacitor are for start and run in the Steinmetz type 2(delta) circuit, where Cr and Cs are what you might expect ie:

[ElectriciansForums.net] How to wire motor plug

What you see is a switch which introduces the start capacitor during run up and then disconnects it at operating speed. The grinder motor has no internal switch to do this and the rotary switch cannot be co-opted to do it. The customization overcomes the absence of the switch by wiring the motor as the red circuit drawn below which keeps Cs in circuit . The way winding W is fed via winding V reduces the potential across W to prevent it overheating when permanently fed via the low series reactance of Cs which although its value cannot be seen is normally of the order 200uF. By contrast the run capacitor is 25uF so a higher series reactance. Tracing out the machines current wiring one arrives at the circuit I point to in the middle of this scribbled diagram, where LN are across U:



[ElectriciansForums.net] How to wire motor plug

I have not had time to think about whether the rotary switch can be used to provide REV- OFF-FWD control - perhaps others might think on this.
 
Last edited:

Reply to How to wire motor plug in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

It would certainly heat up faster at 240V! I have a large 240-120V transformer to power my American kitchen appliances here.
Replies
12
Views
374
Most appliances come with a plug fitted if they are rated 13amp.or under. If not I would just fit a plug top. If it's rated greater than 3kw then...
Replies
1
Views
1K
That will work fine as long as the Pirs use relay switching, some don't.
Replies
2
Views
345
  • Question
I know this post is nearly 6months old but its essential for future readers of this thread to be reminded here what the OP is suggesting is not an...
Replies
3
Views
1K
Hi James, At the inverter end the multi strand is ferruled and torqued in the terminal and at the motor end they are the “wago type” push fitting...
Replies
2
Views
306

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks