I have just completed an EICR.
The install is TT, Ze is 308 ohms.
Zs on all circuits is <1.5 ohm due to bonding.
There is an up front 30mA RCD which trips with the push button but does not trip when tested either at a socket, light or actually in the RCD itself.
I know the RCD is faulty as I had a spare RCBO which I used and tripped as it should.

The lighting circuit had N-E IR readings of 0.27ohms. All other circuits were >2M ohms.

My question is why did the RCBO not trip instantly when I powered up this circuit through the RCBO?
 
Yes, Zs was tested with bonding connected to MET, so the blasted fault current was just coming back through the neutral due to the fault!

This is what was happening when the RCD was being tested as well. There was no imbalance because the current I produced when testing was coming back through the neutral which was a much more attractive path than the 300ohm rod, again due to the fault! I wonder what Ra would be needed to counteract this!

I do appreciate you explaining that Dave.

Now it's got me thinking more..

Has this happened in this case due to the fault being so bad, i.e 0.27ohm (and in effect joining the earth to the neutral)?
If the IR had been higher, lets say 500ohms or even 6000ohms (both of which should trip an RCD) would the RCD have tripped? I guess we'd have to do some maths, but I expect there would be an exact theoretical IR figure where the RCD would start tripping (depending on the relationship between the Ra of the rod and the degree of severity of the IR fault)?

What Ra would be needed to counteract this?
The short answer is that there isn't a value of Ra which could counteract this fault. The fault is a resistance in parallel with the fault, so assuming a theoretical textbook situation rather than the real world:
With the return path of 1.5 ohms via the fault an equal Ra of 1.5ohms the ratio of current flow is 1:1 so a 30mA RCD would need a 60mA fault to trip it.
With an Ra of 0.15 the ratio would be 1:10 so your 30mA RCD would need a 33mA fault to trip it (if my mental maths is working today)
Obviously in the real world RCDs trip at less than 30mA,usually 27ish, so you could in theory get Ra low enough to still have it trip at 30mA,but you'd be looking at an Ra of a fraction of an ohm which is quite tough to achieve without a lot of buried metal.

You can apply a similar answer to your next question.
If the fault was 300ohms and your Ra is 300ohms you would again get the 1:1 ratio. So as the resistance of the fault goes up you will reach a point where its effect becomes negligible on the tripping of the RCD.

With this fault on the system most of the circuits may now appear to have a Zs low enough to allow the mcbs to provide fault protection, apart from the minor issue that all the fault current will be going via the 1mm cpc and neutral of the lighting circuit,provably causing quite a bit of thermal stress.
 
Also, does this mean that on a TT with a poor Ra, if there is a dead short between N-E on one of the circuits, then an up front RCD will never trip when tested (with main switch still on)?

Even on a TT with what is generally accepted as a good Ra this will happen. And it's not just that it won't pass a test, it won't trip on fault.

I think one of the reasons why I object to the 'TTing' of outbuildings without a very good reason is becoming clearer.
And also why I get very annoyed with the 'regs say 200ohms' 'one rod is enough' attitudes towards TT systems.

Dare I raise the subject of SPSN RCBO's at this point?
 
Even on a TT with what is generally accepted as a good Ra this will happen. And it's not just that it won't pass a test, it won't trip on fault.

I think one of the reasons why I object to the 'TTing' of outbuildings without a very good reason is becoming clearer.
And also why I get very annoyed with the 'regs say 200ohms' 'one rod is enough' attitudes towards TT systems.

Dare I raise the subject of SPSN RCBO's at this point?
I was thinking that a little earlier. I've always thought whats all the fuss with 200ohms when 1667 is all that is required. 200 is almost definitely going to be stable enough not to exceed 1667 even with the driest of conditions. However, even though a much smaller Ra (say <20ohms) would still not have been sufficient in my example to enable to RCD to trip, it would in far more cases than 200ohms.
 
I was thinking that a little earlier. I've always thought whats all the fuss with 200ohms when 1667 is all that is required. 200 is almost definitely going to be stable enough not to exceed 1667 even with the driest of conditions. However, even though a much smaller Ra (say <20ohms) would still not have been sufficient in my example to enable to RCD to trip, it would in far more cases than 200ohms.

Yes you can't guard against it 100% as it becomes an endless cycle of 'what if' and 'how many faults can you protect against at once'.

On balance I think I'd rather see a focus on using SPSN RCBO's on all circuits. Your fault would still not trip the RCBO for that circuit, but as soon as another fault occurs it should trip.
 
However, even though a much smaller Ra (say <20ohms) would still not have been sufficient in my example to enable to RCD to trip,

It's actually Zdb that matters for how much the N-E fault affects RCD operation, not the Ra. If there is any low impedance path from the MET, then the current will flow through that just as well as through the actual earth electrode, so a high Ra doesn't inherently mean the RCD is completely disabled. Also important is the resistance of the circuit between the DB and the N-E fault. The higher the resistance, the less the leakage (on other circuits) will divert to the neutral and the less impact the fault will have.

Here is another peculiarity to think about. Shock faults to true earth not involving the CPC, e.g. touching a damaged lawnmower cable standing barefoot in the garden, create a normal unbalanced current in the RCD because in the absence of the CPC there is no parallel path to neutral via the N-E fault. However, the RCD is measuring the algebraic sum of line and neutral current, including leakage in both conductors. This will be made up of the shock current (via the RCD line terminal) and some current from the neutral bar going to earth at the fault (via the RCD neutral terminal). These will tend to be in phase, both flowing through the RCD in the same direction, in which case they will cancel out. The RCD might therefore trip without leakage occurring from the line, or not trip with leakage occurring from the line, or anywhere in between, depending on the magnitudes of the currents.
 
Always good to give an update!

Identified the problem circuit, broke it down in a couple of hours to between 2 points.

It was between a wall switch for a wall light (containing PL and N) and a ceiling pendant. Approx 50cm (DIRECTLY) above the switch was the wall light, with a screw that looked suspiciously directly in line with the PL+N cable. Removed the screw and the fault disappeared! Always feels good doesn't it when you find it, especially when it's a very visible problem that you can show the customer.

Oh yes, and the RCD trips as it should do now when tested. Actually, I better rephrase that otherwise I'll get a few damns from DaveS :D . The RCD always tested fine when tested correctly with all outgoing cables disconnected. It now even tests with them connected :).

[ElectriciansForums.net] Why isnt the RCD tripping?

A big thankyou to all those who replied, especially @Lucien Nunes and @davesparks who as usual gave very useful advice.
 
Always good to give an update!

Identified the problem circuit, broke it down in a couple of hours to between 2 points.

It was between a wall switch for a wall light (containing PL and N) and a ceiling pendant. Approx 50cm (DIRECTLY) above the switch was the wall light, with a screw that looked suspiciously directly in line with the PL+N cable. Removed the screw and the fault disappeared! Always feels good doesn't it when you find it, especially when it's a very visible problem that you can show the customer.

Oh yes, and the RCD trips as it should do now when tested. Actually, I better rephrase that otherwise I'll get a few damns from DaveS :D . The RCD always tested fine when tested correctly with all outgoing cables disconnected. It now even tests with them connected :).

View attachment 51925

A big thankyou to all those who replied, especially @Lucien Nunes and @davesparks who as usual gave very useful advice.
Just read all of this topic and this is one of the main reasons why I joined this forum to learn from the more experienced and intelligent sparkys had to read the posts a few times to understand but now I do another tick off the box ?
 

Reply to Why isnt the RCD tripping? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Ok I’ll try this when I’m down
Replies
4
Views
285
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
445
davesparks
D
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
557
  • Question
As you said in #9 get an electrician involved. The information you are giving is not clear as you do not understand what is being asked which...
Replies
10
Views
984
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
635

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks