I finished framing my bathroom and wired an outlet and switch. I want to connect a 20 amp circuit breaker to the panel. I know the black hot wire is connected to the circuit breaker and it snaps into the panel. Does the ground and nuetral wire connect to the bar on the left? I see there is a mix of nuetral and white wires. Does it matter what order?
 
View attachment 53821
I finished framing my bathroom and wired an outlet and switch. I want to connect a 20 amp circuit breaker to the panel. I know the black hot wire is connected to the circuit breaker and it snaps into the panel. Does the ground and nuetral wire connect to the bar on the left? I see there is a mix of nuetral and white wires. Does it matter what order?
Rube08 yes you can hook both the white wire and the green wire to the same bar. That’s looks like the first panel after the power company
[automerge]1573598515[/automerge]
Rube08 yes you can hook both the white wire and the green wire to the same bar. That’s looks like the first panel after the power company

No it doesn’t matter in what order but I always hook up the ground first then the neutral and last is black
 

Reply to Help with adding a circuit breaker in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
There is nothing inherently wrong with this part of the layout. There is another option that you may want to consider. Those supply conductors...
Replies
3
Views
1K
  • Question
I appreciate the input on this. I decided it is not a good idea, and will spend the money and time to install a new dedicated circuit with...
Replies
5
Views
1K
Ok, please be aware that I am a 'do-it-yourself-er,' so if this isn't the right place to be posting this thread, let me know where I should be...
Replies
0
Views
359
  • Question
It sounds like there is damage to the wiring underground. Do you know what kind of cable was used, in any underground wiring is used has to be UF...
Replies
3
Views
573
The power company only brings in 3 wires which is 2 live and 1 neutral wire. It’s our responsibility to add the ground rod to bond the neutral...
Replies
3
Views
539

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks