Stevey you can’t add all your breakers. What is meant by quad is slim line breakers. Regular breakers are 1 inch and slim line breakers are 1/2 inch so you can install 2 for one. Quit worrying about overloading your panel if you add all the breakers it will certainly be over 200 amps but if you would put an amp probe on your panel you probably are not going to pull over 60 amps at the most. I’ll explain it like this you have what’s called a calculated load which is what you see on your breakers then you have a connected load. With that said that you will not be having all breakers pulling amperage like your hot water heater, oven, dryer, heat, air conditioner, microwave will not be pulling amperage on all breakers at the same time. I hope you understand what I just told you and quit worrying
[automerge]1591228941[/automerge]
Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.
[automerge]1591229012[/automerge]
Stevey no matter what name brand panel you have look under the cover at the factory sticker. It has the style and type breakers you can use plus the torque requirements. A lot of different name brand breakers will work but if an inspector sees that that particular breaker is not recommended he or she will fail your installation and will not let you have power until it is corrected.