Basic question..jist trying to gain some knowledge.
I have 2 breaker boxes in my home. Each have 100 amp main breakers.
One is not a sub to the other. Both are serviced directly from the meter outside.
Should I assume that my house has a 200 amp service coming in? Just split between the 2 boxes? Upstsirs box primarily operates items on that floor, and 2nd box does same for basement.
Thank you in advance for replies.
 
There’s normally a service fuse BEFORE the meter. That will dictate the total load.
It could be 100A or more likely 80. Possibly only 60.
A 100A mainswitch in a consumer unit is just a rating. It can cope with 100A safely. It’s not a circuit breaker that would trip out at 100A.
I’ve just read you’re in Baltimore, so things might be different than UK.
One of our American members might help
 
There’s normally a service fuse BEFORE the meter. That will dictate the total load.
It could be 100A or more likely 80. Possibly only 60.
A 100A mainswitch in a consumer unit is just a rating. It can cope with 100A safely. It’s not a circuit breaker that would trip out at 100A.
I’ve just read you’re in Baltimore, so things might be different than UK.
One of our American members might help
Thank you for reply!. I didnt even think about the US/UK thing. But overall what you're saying makes sense.
 
Basic question..jist trying to gain some knowledge.
I have 2 breaker boxes in my home. Each have 100 amp main breakers.
One is not a sub to the other. Both are serviced directly from the meter outside.
Should I assume that my house has a 200 amp service coming in? Just split between the 2 boxes? Upstsirs box primarily operates items on that floor, and 2nd box does same for basement.
Thank you in advance for replies.
BlackwidowZ71 I hate to tell you this but I can tell you what you have without looking at it. It sounds like You have a 100 amp panel located outside , you also have another 100 amp panel being sub fed inside your house from your main panel. I’ve never seen the power company or the inspector let you split bolt 2 separate panels on the load side of the meter without short circuit protection
 
BlackwidowZ71 I hate to tell you this but I can tell you what you have without looking at it. It sounds like You have a 100 amp panel located outside , you also have another 100 amp panel being sub fed inside your house from your main panel. I’ve never seen the power company or the inspector let you split bolt 2 separate panels on the load side of the meter without short circuit protection
Picture attached. I have 2 separate lines from meter to each panel box.
 

Attachments

  • [ElectriciansForums.net] Incoming service amperage?
    20201014_070337.jpg
    61.4 KB · Views: 27
I’m sorry I stand corrected. I’ve never seen a single family dwelling made up like that
Yes sir, its bizarre. Im not an electrician, but in my 22 years as a fireman..Ive never seen a single residential home like this. My home is split foyer, and when I moved in... there were originally 2 front doors..Im assuming at one point the intent was a basement level area and upstairs seperate. I guess it would be safe to assume that I dont have total 200 amp service to entire home..just 100 amps each for both levels of home.
 
Yes sir, its bizarre. Im not an electrician, but in my 22 years as a fireman..Ive never seen a single residential home like this. My home is split foyer, and when I moved in... there were originally 2 front doors..Im assuming at one point the intent was a basement level area and upstairs seperate. I guess it would be safe to assume that I dont have total 200 amp service to entire home..just 100 amps each for both levels of home.
I guess you would be 2 separate 100amp boxes. Look on the bright side, you still in theory have 200 amps and a lot of spare spaces to add something
 

Reply to Incoming service amperage? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
As long as you have a 200 amp main panel then there is no problem feeding a 200 amp sub panel. I’m assuming that you have a 100 amp sub panel and...
Replies
1
Views
1K
  • Locked
I'm going to lock this thread. What you're doing is blatently hazardous and likely to cause injury to yourself, an occupant of the house or even...
Replies
4
Views
1K
  • Question
I think that you have already figured it out. Good luck with your project
Replies
1
Views
2K
  • Question
Pictures would be nice but do not change that breaker to a 90 amp. You can buy slim line breakers and free up space. Just because you have to...
Replies
1
Views
1K
  • Question
You can splice at the first or second ground rod but you will need an extra tear drop or acorn for a 5/8 ground rod. You are allowed only on wire...
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks