Smart Switch lighting neutral question | on ElectriciansForums

Discuss Smart Switch lighting neutral question in the UK Electrical Forum area at ElectriciansForums.net

dmleonard

DIY
Joined
Nov 14, 2020
Messages
2
Reaction score
0
Location
Minneapolis, MN
I own a commercial storage unit where I keep my boat, trailers, etc. I went to install a Smart Switch in it, so I could remotely control the lights if needed (i.e. some times I will forget to turn them off when I leave). I bought a witch, took the cover off, and realized I don't have a neutral (or so, I think). But it is not as simple as just having the neutral up at the light. Running a neutral would not be feasible as it is about a 70 ft run through a mix of EMT, flexible, and inside the wall. So I bought a switch that doesn't need a neutral, but that didn't work because the unit has non dimmable LED lights.

Anyway, I am trying to get my bearings about how this is wired and cannot figure out what it looks like up in the box at the ceiling (23 ft high and not easily accessible). It is a 2 gang wall box, with a light switch and a variable speed fan switch. They share a common 20 amp breaker and a single hot. That is about as far as I can figure out. I have attached a diagram. If anyone can shed some light on how this is all wired up, I would greatly appreciate it.
 

Attachments

  • [ElectriciansForums.net] Smart Switch lighting neutral question
    grondo wiring.jpg
    43.1 KB · Views: 22
Yes, you are correct, there is no neutral at the switch position. Just one hot in and two controlled hots out. It might be possible to use the smart switch that does not need a neutral, if you can access the light fitting to add some load, possibly an artificial load a.k.a snubber, or a small filament lamp. that will pass enough current to keep the smart switch operational.
 
Thanks for confirming. This is where I start to get confused. The smart switch came with a snubber for a standard light bulb, but that doesn't do me much good for my hardwired overhead LED light panels. Shouldn't the fan being on (I never turn it off) accomplish the same the same thing since they share the same circuit?
 
No, the fan is irrelevant here, as it is not controlled by the smart switch. You need a hardwired snubber that would be connected into the same wires as the LED panel, its purpose being to drain off the small standby current that the smart switch would otherwise be trying to pass through the panel.
 

Reply to Smart Switch lighting neutral question in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

brilliant thanks for your support. Lee
Replies
8
Views
567
  • Question
Firstly I would suggest that of the three sets of cables, they are not all 'incoming'. There might be one cable (of 3 wires) bringing in permanent...
Replies
1
Views
749

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top