Also, would it be to much to ask for a pic of the table regarding distributed and none distributed neutrals?
The problem is after the 1st fault you might have 133V to earth (if N-E faulted) or you might have 230V to earth (if either of L1-L3 are faulted).So basically TN vs IT? I can't picture at 133/230Y TN system needing the same disconection time as 230 volt IT. Both are none distributed neutral systems.
Right, but picture a 133/230Y TN system. Highest voltage to earth will be 133 volts no matter the network conditions.