Hi everyone,

Completed EICR for property recently and found there is a hole in the service head on neutral side, meaning live parts accessible by a finger. Photo attached.

Does anyone knows best way to repair it? I've tried to find replacement element but couldn't find anything.

Many thanks
 

Attachments

  • [ElectriciansForums.net] Service head EICR
    IMG_20210318_112319.jpg
    519.6 KB · Views: 235
You say that but they do have an affect on how the inspector would perceive risk, it's why we have an external influence code for persons; from children up to skilled person.

Does it make me a bad engineer for going outside of the guides and documents we're told to work to, or does it make me a more con-che-n-tious (can't spell the word) engineer for looking at the bigger picture and wanting to have a better understanding as to why things are the way they are, why we have cutouts like these and why a missing cover is acceptable on 1 area but not another; I'm thinking diverted neutral currents going into the property and that section that is accessible becoming live, sure it's s million to one chance but so long as I can say I've done what I can to sort it, then I sleep better, if the DNO want to shrug and walk away, that's on them.
In a house full of bonded metalwork and earthed appliances, it's hard to see how covering up that small piece of exposed metal will be of benefit should the DNO's neutral go OC.
 
This is seen at a vast majority of cutouts and is normal practice. And TBH it does make me worry that some people that are carrying out EICRs don't have the understanding of what is required and how to code the so called issues
Indeed. Like in this photo:

[ElectriciansForums.net] Service head EICR


This is no different from a safety point of view to the OP's photo. No code. No comment necessary.
 
You say that but they do have an affect on how the inspector would perceive risk, it's why we have an external influence code for persons; from children up to skilled person.

Does it make me a bad engineer for going outside of the guides and documents we're told to work to, or does it make me a more con-che-n-tious (can't spell the word) engineer for looking at the bigger picture and wanting to have a better understanding as to why things are the way they are, why we have cutouts like these and why a missing cover is acceptable on 1 area but not another; I'm thinking diverted neutral currents going into the property and that section that is accessible becoming live, sure it's s million to one chance but so long as I can say I've done what I can to sort it, then I sleep better, if the DNO want to shrug and walk away, that's on them.

It is a no code. Not even an observation. Not an issue. No potential dangerous Situation. No need to contact DNO.

The point I was trying to make earlier was that I am concerned, but not about the cutout,

I am concerned and gobsmacked that anyone carrying out EICRs would not know this Was normal for a cutout. There is absolutely nothing wrong with it.
 
It is a no code. Not even an observation. Not an issue. No potential dangerous Situation. No need to contact DNO.

The point I was trying to make earlier was that I am concerned, but not about the cutout,

I am concerned and gobsmacked that anyone carrying out EICRs would not know this Was normal for a cutout. There is absolutely nothing wrong with it.
I know it's true that not any one of us sparkies knows everything and has come across every type of installation practice, but this reinforces a comment I, and others, have made in several different threads on the subject of EICRs and who should be doing them.
And that is, inspection and testing requires, not only technical knowledge gained through formal training, but actual experience of the types of installation that you are inspecting. This kind of experience only comes with time, and preferably working alongside someone who has that experience.
Without such experience, how can a person pass judgement and award an appropriate code?

This current thread is a case in point. To me, and to several others who have commented, it's obvious what the recommendation should be, and if you have to ask.......
 
Last edited by a moderator:
Question to Op did you find any other deviations when doing the EICR ?
If so do you want to share on here?
Apart from that there is no RCD protection on all circuits except one (kitchen ring). Circuit supplying bathroom (light, extractor, shaver socket) no rcd and no supplementary bonding present.
Client willing to upgrade consumer unit
Rest of the installation is fine with all visuals test result satisfactory.
 
So what about this one:

View attachment 83535

Apparently a new meter was fitted couple of months ago, and it seems the meter fitter taped up the earth block, rather than fit the insert/cover. The tape has now come off. The customer is sure that the cover was not missing before.

My guess is the part perhaps fell of during fuse removal, fell to the concrete floor below and cracked.

I'd say that once the service head is compromised compared to how it was originally installed, then it should be at least raised with the DNO so that they can decide whether the integrity as a whole is up to their standards - since it does belong to them. That way they do the risk assessment and take responsibility.

On an EICR you are ticking to say the service head is satisfactory (or not) after all - and without further investigation I'd not be 100% sure that there was no access to an actual live part in your case....

One I raised with the DNO just yesterday

[ElectriciansForums.net] Service head EICR

where the shroud is coming away and although it's "only" the PEN stranded that is visible that may not be the case in the future - and I'd have no idea whether a long thin finger could reach other more dangerous parts.

Because the DNO equipment (service heads in particular) is usually kept at a distance from official training (at least at domestic level), it's sometimes hard to gain the experience or information necessary to do a proper risk assessment.

I'd happily do a course with the DNO that gave me some more insight - perhaps with the right to risk assess and pull fuses officially when needed (with temporary reseal to be checked by DNO staff if necessary) - and quicker access to resources when a problem occurs without having to wait in line on 105 with the householders who's kettle isn't working...
 
Because the DNO equipment (service heads in particular) is usually kept at a distance from official training (at least at domestic level), it's sometimes hard to gain the experience or information necessary to do a proper risk assessment.

I'd happily do a course with the DNO that gave me some more insight - perhaps with the right to risk assess and pull fuses officially when needed (with temporary reseal to be checked by DNO staff if necessary) - and quicker access to resources when a problem occurs without having to wait in line on 105 with the householders who's kettle isn't working...
If they trained and gave you their blessing then they'd be liable when something goes wrong, and when half your networks is so far past its service life its in many cases quite literally falling apart that's a big ask.

Much, much nicer for them and their shareholders to maintain the pretence that nobody ever touches it even though we all know its BS.
 
Never seen a non dno sparky wearing the official ppe for working on a cut out, ie rubber gauntlets, leather over gauntlets, full face visor, and non combustible clothing. Not saying dno empoyees always do.......
 
It is a no code. Not even an observation. Not an issue. No potential dangerous Situation. No need to contact DNO.

The point I was trying to make earlier was that I am concerned, but not about the cutout,

I am concerned and gobsmacked that anyone carrying out EICRs would not know this Was normal for a cutout. There is absolutely nothing wrong with it.

To me this highlights an Issue I have with that whole section(1.0) of the inspection schedule.

It is not the responsibility of the electrician, we have no right to work on it yet we are supposed to have the knowledge to diagnose faults and record them and are expected to report them to the DNO.

This is their equipment, they charge for its use and should be responsible for monitoring its condition, you know, maybe a cursory once over once a year whilst reading the meter. ?

The dozens of interactions I've had with DNO faults have all been billed to the customer for my time, is this right?

Now back to the OP, is it fair to expect an inspector to have in depth and historic knowledge of the many, many intake and metering configurations and devices and be able to competently assess their condition?

It's not straight forward as no sane spark is going to start work on an installation with a smouldering intake but an exposed terminal?, a cracked cover?, unsupported tails?

It would be an interesting test case if for every certificate we issued we invoiced the DNO an inspection fee.

Rant over.
 
Did you not use to have Darth Maul, Darth Tyrannus and Darth Vader as your apprentices at one point? ;)
I taught them well, young Jedi. they are now all on the Dark side (of the moon, with Syd Barrett).
 

Reply to Service head EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
My GF asked the bartender for a double entendre, so he gave her one.
Replies
12
Views
2K
loz2754
L
  • Article
EMailed to the forum for you @PCBWay
    • Winner
Replies
1
Views
1K
  • Question
Hello Dave, Thanks for taking the time to reply. I appreciate the info, I haven't updated this post yet, but I have since been talking to some...
Replies
3
Views
1K
I guess my last post was even less direct than intended.
    • Like
Replies
11
Views
591
nicebutdim
N
Try disconnecting the "central heating off" wire from terminal 2 and insulate it (eg Wago connector or choc block or similar) and tuck it out of...
2
Replies
32
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks