Dear All,
I was helping a friend to fit a new French window lock when she showed me her crazy downstairs lighting - she has just moved into the house which was built in the 1970's and there are lots of things wrong with it. Is there a quick fix for the following:
Please see the Pdf : there is a 2 gang switch (A on the pdf) which when operated ALONE operates a ceiling spotlight On and Off (1st gang) when operated Alone the 2nd Gang A works the uplighter On and Off.
There is a three gang switch (B on pdf) on the opposite side of the room which: 1st Gang B is linked to both Gangs in A and produces the following:
If 1st Gang A is ON (spotlight) then 1st Gang B Will switch OFF the spotlight but NOT switch it ON
If 1st and 2nd Gang A are On then 1st Gang B will switch the spotlight On and OFF
If 2nd Gang A is On (Uplighters On) then 1st Gang B switches Uplighters off
If 1st and 2nd Gang A are ON (both spotlight and uplighter) 1st gang B will flick between switching the Spotlight and Uplighters ON and OFF !!
If 1st Gang A (spotlight is OFF) and 1st Gang B is used to switch Uplighters ON then 2nd Gang A ( the control for uplighter) will NOT switch the Uplighters OFF.
I am attaching pictures of the wiring behind A and B
The three Gang B switch should allegedly operate as a two way switch for the Uplighters and Spotlight and a two way switch for the landing light upstairs. The middle switch appears to just feed a lonely single uplighter - which can't be right either ?
The 2 Gang switch is marked A$A and MKD on the rear and the 3 Gang switch I can't find a make for.
Any suggestions would be gratefully received.
I was helping a friend to fit a new French window lock when she showed me her crazy downstairs lighting - she has just moved into the house which was built in the 1970's and there are lots of things wrong with it. Is there a quick fix for the following:
Please see the Pdf : there is a 2 gang switch (A on the pdf) which when operated ALONE operates a ceiling spotlight On and Off (1st gang) when operated Alone the 2nd Gang A works the uplighter On and Off.
There is a three gang switch (B on pdf) on the opposite side of the room which: 1st Gang B is linked to both Gangs in A and produces the following:
If 1st Gang A is ON (spotlight) then 1st Gang B Will switch OFF the spotlight but NOT switch it ON
If 1st and 2nd Gang A are On then 1st Gang B will switch the spotlight On and OFF
If 2nd Gang A is On (Uplighters On) then 1st Gang B switches Uplighters off
If 1st and 2nd Gang A are ON (both spotlight and uplighter) 1st gang B will flick between switching the Spotlight and Uplighters ON and OFF !!
If 1st Gang A (spotlight is OFF) and 1st Gang B is used to switch Uplighters ON then 2nd Gang A ( the control for uplighter) will NOT switch the Uplighters OFF.
I am attaching pictures of the wiring behind A and B
The three Gang B switch should allegedly operate as a two way switch for the Uplighters and Spotlight and a two way switch for the landing light upstairs. The middle switch appears to just feed a lonely single uplighter - which can't be right either ?
The 2 Gang switch is marked A$A and MKD on the rear and the 3 Gang switch I can't find a make for.
Any suggestions would be gratefully received.