Is there anything preventing us from using these type of RCDs for a 55-0-55 circuit?

the picture shows the original set up.
 

Attachments

  • [ElectriciansForums.net] Using double pole RCD
    B1750BD0-0A9A-407F-9E5D-FBCB2AFFE2B0.png
    538.2 KB · Views: 58
  • [ElectriciansForums.net] Using double pole RCD
    E75F2EF9-0960-4389-AD32-6C9CF5AA34F5.jpeg
    356.5 KB · Views: 58
OP perhaps you can clarify. Are you proposing to use the RCD to replace the Vigi residual tripping actuator but leave the original DP MCB in service, or what?
 
I suppose my question wasn’t clearly explained sorry for my mistake. The question I really wanted to ask is really other than the fact the RCD in the photo is mechanical interlocked with the D1 breaker would the RCD function for a 55-0-55 supply. I know normally we’d L-230v
N-0v Also am I being silly here but if you could get a RCBO that size could that be fitted? Also what is the reason for this kind of set up overload protection and additional protection?
 

Reply to Using double pole RCD in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Which rcd is it? Is it one for everything, one for a few circuits?
Replies
5
Views
357
  • Question
Wallbox Fuse Box Lite Single Phase has anyone used one of these? I've installed one feeding a Pulsar Max, the Pulsar Max is set to 32Amp max. The...
Replies
0
Views
459
Given that, it probably makes sense to TT the shed, unless you can be sure it doesn't act as an extraneous-conductive-part. (The SWA won't have...
Replies
10
Views
529
  • Question
Wylex and Crabtree miniature RCBO’s are all SP and switched neutral. Can get them around £18.00 if you look online.
2
Replies
28
Views
5K
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
961

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks