Would be interested to know how people would code this:
Upstairs bathroom - with pull cord and shower switch above 2.25 (just)... but over the edge of the bath below shower. Not in a location where they are likely to be sprayed with water unless someone is really trying...
6mm cable to shower running down directly between tiles and cold feed to shower.
Shower is RCD protected, but bathroom lighting circuit currently isn't - (that's already a C2 which will be fixed with RCBO on that circuit).
The Cable not separated from 'non-electrical services' seems like a C3 to me, since it's RCD protected.
Switches are clearly not in a good location - and I feel I should note that, but not sure they reach a C2 level.
Seen some discussion on here years ago about the cords, but the shower cord does actually have that plastic 'piece' in, which I believe is meant to provide some insulation from a wet cord scenario? The upper bit probably does fall within Zone 2 by mm....
Upstairs bathroom - with pull cord and shower switch above 2.25 (just)... but over the edge of the bath below shower. Not in a location where they are likely to be sprayed with water unless someone is really trying...
6mm cable to shower running down directly between tiles and cold feed to shower.
Shower is RCD protected, but bathroom lighting circuit currently isn't - (that's already a C2 which will be fixed with RCBO on that circuit).
The Cable not separated from 'non-electrical services' seems like a C3 to me, since it's RCD protected.
Switches are clearly not in a good location - and I feel I should note that, but not sure they reach a C2 level.
Seen some discussion on here years ago about the cords, but the shower cord does actually have that plastic 'piece' in, which I believe is meant to provide some insulation from a wet cord scenario? The upper bit probably does fall within Zone 2 by mm....