Discuss Coffee machine wiring 3 phase on single phase circuit in the Electrical Engineering Chat area at ElectriciansForums.net
No it’s single phase mateIs there 3 phase available at the property?
Then it can not be done.have spoken to the customer or are you it.This coffee machine is three phase model number sm 105e
It’s three phase with 3 brown cables one neutral and earth
What is the cheapest way to wire it in?
thanks
doesn’t have name plate I checked instructions onlinesome machines can be wired for single phase.
check the name plate and instructions
Thanks James just got the correct manual now just wondering if I can spur off the 16a 2.5mm plug socketHaving a quick look online, it looks like it can be configured for single phase.
you need to get the correct manual for that model.
however it is between 5 and 7.5kw
so you are going to need some bigger cables than we can see in the picture!
So if I use this rotary isolator and spur off a 32a ring main and then terminate the coffee machine into the load sideI think a 32A socket and rotary isolator would be the way forward.
maybe a dedicated rcd would be good.
I really think you need to get a professional in to look at this.So if I use this rotary isolator and spur off a 32a ring main and then terminate the coffee machine into the load side
Ok no problem going to leave it then just checkingYou cannot be spurring off a ring final circuit for a load of that nature it needs a dedicated supply.
Reply to Coffee machine wiring 3 phase on single phase circuit in the Electrical Engineering Chat area at ElectriciansForums.net
