What is Zone 1, 2 and 3 in wet locations? What does class 1 mean? Can someone educate on why, what and how this applies to kitchens and bathrooms?
 
regulations specify what we can, and cannot, fit in each zone.

class 1 equipment or appliances are generally those which have metal (conductive) casings etc.and must be earthed. class 2 are double insulated and/or non-conductive encolsures.
 
Be clear Zones and classes are very different things

Zones - as Tel indicates: refers to different areas within an area containing a bath etc.
Class - (electrical) : a description of the insulation/earthing of the item
Class - (IP) : a measure of ingress protection against mechanical and water penetration.

So the Regs specifies that in Zone "x" any electrical item must have IP Class "y" if electrical class "z", or IP Class "a" if electrical class "b" etc and/or which electrical classes are not permitted and/or which IP classes are not permitted.

It has been somewhat simplified recently both in terms of Zones and what is acceptable IP and electrical classes
 
Be clear Zones and classes are very different things

Zones - as Tel indicates: refers to different areas within an area containing a bath etc.
Class - (electrical) : a description of the insulation/earthing of the item
Class - (IP) : a measure of ingress protection against mechanical and water penetration.

So the Regs specifies that in Zone "x" any electrical item must have IP Class "y" if electrical class "z", or IP Class "a" if electrical class "b" etc and/or which electrical classes are not permitted and/or which IP classes are not permitted.

It has been somewhat simplified recently both in terms of Zones and what is acceptable IP and electrical classes


Makes sense. Is there by chance a table of what combinations are allowable?
 
regulations specify what we can, and cannot, fit in each zone.

class 1 equipment or appliances are generally those which have metal (conductive) casings etc.and must be earthed. class 2 are double insulated and/or non-conductive encolsures.


Where do RCDs fit into all this? Are they effected by either zone or IP rating?
 

Reply to Zone 1, 2 and 3 in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Thank you..... & did have all the fan isolator/ fuse in same plate (click) so quinetic wouldn't worked on this occasion
Replies
12
Views
633
Unfortunately I don't think you will get an "off the shelf" diagram for the system you are trying to do The Wiser system is very adaptable but it...
Replies
1
Views
298
I thought that too, but I didn’t want to upset the old fella by telling him 😛
Replies
6
Views
1K
At some point, all sewage pumps will fail, or need extensive maintenance. I make it quite clear that I'm not interested in either.
Replies
16
Views
900

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks