New consumer unit for garage | on ElectriciansForums

Discuss New consumer unit for garage in the UK Electrical Forum area at ElectriciansForums.net

Joined
Sep 17, 2020
Messages
47
Reaction score
8
Location
London
Hello everyone,

A new small DB will be installed inside a garage for few lights and sockets. The feed will come from inside the house. Does it need to be an IP65 unit or can be the usual metal clad?

Thank you
 
Depends on if you think a metal clad is inappropriate for the environment. Either is fine.
 
Unless it is near a doorway where rain could get in (say 45 deg angle), or a known leaky roof, or where someone uses a sink/pressure washer, then I would not worry about meeting IP65.

But if it is only lights and a couple of sockets, and the house CU is already on RCD or RCBO supply, then why not just feed the sockets directly as a radial from a 20A supply and have a 3A FCU to switch the lights off that?
 
Unless the garage is attached to the main house. In which case the new consumer unit should probably be made of non combustible material.
Unless the garage is not part of the domestic premises

[ElectriciansForums.net] New consumer unit for garage

and is not meant to be used by the people who live in the house, then 421.1.201 applies, whether it's attached or not.
 
Unless the garage is not part of the domestic premises

View attachment 84646
and is not meant to be used by the people who live in the house, then 421.1.201 applies, whether it's attached or not.
Fair point.
There was an article in one of the trade journals considering this. It suggested there may be a case for not applying 421.1.201 in out buildings that are not directly attached to the house.
But it depends, like so many things, on how we interpret the regulations...
 
Fair point.
There was an article in one of the trade journals considering this. It suggested there may be a case for not applying 421.1.201 in out buildings that are not directly attached to the house.
Hard to think what that case might be apart from "we don't want to have to apply it."


But it depends, like so many things, on how we interpret the regulations...
I tend to come down on the side of "interpreting" things on the basis of what the actual words are and what the definitions of those words are.
 
It’s only a garage..... just use the last one you took out a house rewire. ?


No. Don’t. Joke.
what a good idea. here's the last one i saved.
[ElectriciansForums.net] New consumer unit for garage
 

Reply to New consumer unit for garage in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
183
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
560
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

  • Question
Personally, I would take a Ze measurement myself rather than rely on someone else's maybe drive by scrap of paper.
2 3
Replies
31
Views
2K
  • Question
What is the distance from the point outside the house to the shed?
Replies
8
Views
761

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top