Is this design exceptable for a Bathroom fan extractor. | on ElectriciansForums

Discuss Is this design exceptable for a Bathroom fan extractor. in the UK Electrical Forum area at ElectriciansForums.net

Tonykakz

DIY
Joined
Apr 15, 2021
Messages
47
Reaction score
1
Location
London
THIS IS FOR ELECTRICAL NEWS ONLY
 

Attachments

  • [ElectriciansForums.net] Is this design exceptable for a Bathroom fan extractor.
    1618504730210-462270975.jpg
    171.4 KB · Views: 157
It's electrically OK, but it would be better to eliminate the junction box and take the feeds for the fan and the light back to the 3A switch/fuse.
There's no switch for the fan, so I take it that it's an automatic one with a humidistat?
You've labelled the pull cord "3 pole isolator". It's single pole and not an isolator with the wiring you show.. It's a switch
 
I assume the feed is coming in from the FCU at the top right? Is the fan an on/off or a timed one? If timed you will want to be sure the switched and permanent live run to the fan.

If this is a bathroom, presumably that's not a standard ceiling rose but a suitable bathroom light?
 
I assume the feed is coming in from the FCU at the top right? Is the fan an on/off or a timed one? If timed you will want to be sure the switched and permanent live run to the fan.

If this is a bathroom, presumably that's not a standard ceiling rose but a suitable bathroom light?
Hi! Thanks . Would you be able to post an a design pic of what you are saying i should follow. Thanks for your time and help.
 
I assume the feed is coming in from the FCU at the top right? Is the fan an on/off or a timed one? If timed you will want to be sure the switched and permanent live run to the fan.

If this is a bathroom, presumably that's not a standard ceiling rose but a suitable bathroom light?
Whats confusing is the manufacturers demanding a FCU be fitted. Currantly the old fan runs on a light circuit with no FCU and islolator. I was going to just fit a 3 pole isolator at the pull cord. But if it requires a FCU i will need to redesign and incorporate the FCU. Thanks for your time and help.
 
It's electrically OK, but it would be better to eliminate the junction box and take the feeds for the fan and the light back to the 3A switch/fuse.
There's no switch for the fan, so I take it that it's an automatic one with a humidistat?
You've labelled the pull cord "3 pole isolator". It's single pole and not an isolator with the wiring you show.. It's a switch
Is this what you mean i should follow.
 

Attachments

  • [ElectriciansForums.net] Is this design exceptable for a Bathroom fan extractor.
    Screenshot_2021-04-15-12-23-03.png
    239.2 KB · Views: 32
A 3pole fan isolator could be used in place of the junction box to enable all poles to be isolated (it does what says on the tin!
The intermediate 3 pole isolator 'junction' would not be needed.
 
Is this what you mean i should follow.
As long as the 'fuse' also incorporates a DP switch (i.e. an ordinary switched fused connection unit), and is placed either inside the bathroom, (outside of the zones), or preferably, immediately outside of the bathroom door the triple pole isolator is not needed.
This circuit does not actually have a light included.
 
As long as the 'fuse' also incorporates a DP switch (i.e. an ordinary switched fused connection unit), and is placed either inside the bathroom, (outside of the zones), or preferably, immediately outside of the bathroom door the triple pole isolator is not needed.
This circuit does not actually have a light included.
Yes this circuit is from thr mains power and is not powered by lighting circuit . Thanks .
 
It's electrically OK, but it would be better to eliminate the junction box and take the feeds for the fan and the light back to the 3A switch/fuse.
There's no switch for the fan, so I take it that it's an automatic one with a humidistat?
You've labelled the pull cord "3 pole isolator". It's single pole and not an isolator with the wiring you show.. It's a switch
How is this design?
 

Attachments

  • [ElectriciansForums.net] Is this design exceptable for a Bathroom fan extractor.
    20210416_120731.jpg
    152.4 KB · Views: 23
How is this design?
That's almost right. (I assume we're ignoring earth for the purposes of the diagram but that it will be there)

The 2 core to the pull cord will be permanent live to and switched live back, so the feed to the light will need to come from the junction box, not the pull cord, so you have switched live and neutral to it.

Many fans don't have the requirement for a 3A fuse, assuming they are running from a 6A MCB, so sometimes it's easier to pick the fan more carefully.

It is also possible to do it with existing lighting wiring, with a Click Mode grid switch, which can contain an isolator and a fuse - or even an isolator and 2 fuses if you need to fuse feed and switched feed separately (though that needs a two gang wide switch).
 
That's almost right. (I assume we're ignoring earth for the purposes of the diagram but that it will be there)

The 2 core to the pull cord will be permanent live to and switched live back, so the feed to the light will need to come from the junction box, not the pull cord, so you have switched live and neutral to it.

Many fans don't have the requirement for a 3A fuse, assuming they are running from a 6A MCB, so sometimes it's easier to pick the fan more carefully.

It is also possible to do it with existing lighting wiring, with a Click Mode grid switch, which can contain an isolator and a fuse - or even an isolator and 2 fuses if you need to fuse feed and switched feed separately (though that needs a two gang wide switch).
Thanks thats great! Yes earthing was ommitted for diagram. Click mode gride switch. Need to look into that to.
 

Reply to Is this design exceptable for a Bathroom fan extractor. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
644

Similar threads

Hi all, first post, please be gentle ;) Iv been involved in a bathroom refurb, nothing major, moving a light fitting and switch. My problem came...
Replies
0
Views
167
D
Hi all, I'm looking for recommendations for a kitchen extractor fan with a rate of 60l/s. We're nearly done with our renovation, but we've just...
Replies
0
Views
167
dimmi1975
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top