Hi all
I haven’t done much of anything with electrics since secondary school (long time) and hoping someone might just double check what I’m saying isn’t totally wrong!

Im building a keg system for home brew using an old chest feeezer. To regulate the temperature I’m using an ink bird ITC 1000 temperature controller. I will attach some pics to illustrate what I’m talking about but essentially I’m chopping up a couple of 2 way adaptors and the plan is...

Mains supply comes in through small hole in freezer, I wire up live and neutral to relevant terminals (1 & 2) for power supply.

Temperature sensor is wired to terminals 3 & 4.

There are then two outputs.

One two way adaptors live and neutral are wired into terminals 5 & 6 for the heating output (little tube heater and pc fan to circulate)

The other two way adaptor live and neutral wired to ports 7 & 8 for cooling output (will feed freezer plug in to it).

I have watched lots of videos and read up abs from what I understand I should combine the earth wires from the three power cables (mains supply, hot and cold outputs to adaptors) and solder and cap off. As I’m not super sure about electrics I thought I should check with people who know before I plough ahead and blow myself up, or worse still waste beer!

Any help much appreciated. Thanks
 

Attachments

  • [ElectriciansForums.net] Join earth wires (from 3 power cables)  together when wiring temperature controller (ITC 1000)?
    C7EE0339-F75B-43B6-9D09-65DE34268848.jpeg
    334.6 KB · Views: 80
  • [ElectriciansForums.net] Join earth wires (from 3 power cables)  together when wiring temperature controller (ITC 1000)?
    83EF78DD-C23E-4334-882F-2CF9CF20B012.jpeg
    543 KB · Views: 47
Hi all
I haven’t done much of anything with electrics since secondary school (long time) and hoping someone might just double check what I’m saying isn’t totally wrong!

Im building a keg system for home brew using an old chest feeezer. To regulate the temperature I’m using an ink bird ITC 1000 temperature controller. I will attach some pics to illustrate what I’m talking about but essentially I’m chopping up a couple of 2 way adaptors and the plan is...

Mains supply comes in through small hole in freezer, I wire up live and neutral to relevant terminals (1 & 2) for power supply.

Temperature sensor is wired to terminals 3 & 4.

There are then two outputs.

One two way adaptors live and neutral are wired into terminals 5 & 6 for the heating output (little tube heater and pc fan to circulate)

The other two way adaptor live and neutral wired to ports 7 & 8 for cooling output (will feed freezer plug in to it).

I have watched lots of videos and read up abs from what I understand I should combine the earth wires from the three power cables (mains supply, hot and cold outputs to adaptors) and solder and cap off. As I’m not super sure about electrics I thought I should check with people who know before I plough ahead and blow myself up, or worse still waste beer!

Any help much appreciated. Thanks


Should also say I’ve got project boxes and trunking so all connections going to be covered.
 
It doesn't read quite like that in the datasheet if it is the itc1000f. The heating and cooling pins appear to be relays, not power sources.

You would have your live feed into 1, 5 & 7. Then pin 6 would go to the live side of your heater. Pin 8 would go to the live side of your chiller. Pin 2 and both your heater and chiller neutrals together to your supply neutral. And your earths from the heater and chiller together with your supply earth.

Then it looks like the relays operate on reaching the thresholds configured on the front end.

At least that's the way I read it.
[ElectriciansForums.net] Join earth wires (from 3 power cables)  together when wiring temperature controller (ITC 1000)?

Edit: although, that doesn't follow their diagram either. Unless pin 2 is meant to be live and pin 1 neutral. It isn't clear of polarity of the supply voltage matters across pin 1 and 2, even in the DC example. Either way, I'd put the live to pin 5 and 7,you wouldn't want to switch on the neutral side.
 
Last edited:
It doesn't read quite like that in the datasheet if it is the itc1000f. The heating and cooling pins appear to be relays, not power sources.

You would have your live feed into 1, 5 & 7. Then pin 6 would go to the live side of your heater. Pin 8 would go to the live side of your chiller. Pin 2 and both your heater and chiller neutrals together to your supply neutral. And your earths from the heater and chiller together with your supply earth.

Then it looks like the relays operate on reaching the thresholds configured on the front end.

At least that's the way I read it.
View attachment 85634
Edit: although, that doesn't follow their diagram either. Unless pin 2 is meant to be live and pin 1 neutral. It isn't clear of polarity of the supply voltage matters across pin 1 and 2, even in the DC example. Either way, I'd put the live to pin 5 and 7,you wouldn't want to switch on the neutral side.

Wow ok thanks glad I asked now!

A little bit worrying that it sounds a bit confusing to someone who knows what they’re doing though!
 
Wow ok thanks glad I asked now!

A little bit worrying that it sounds a bit confusing to someone who knows what they’re doing though!
I'd be clear that I'm not an electrician, and I'm not telling you it would be safe to do that. Just the way that I would interpret the data sheet if I was making it myself.

Did it come with the brown and blue wires attached already? I'd be tempted to use brown for all of 5,6,7 and 8, as they would all be part of the live supply.
 
I'd be clear that I'm not an electrician, and I'm not telling you it would be safe to do that. Just the way that I would interpret the data sheet if I was making it myself.

Did it come with the brown and blue wires attached already? I'd be tempted to use brown for all of 5,6,7 and 8, as they would all be part of the live supply.
No it didn’t, that was me making a start trying to get my plan together and prepping it to be attached.

Ok got you, you probably know a lot more than me tbf.
 
No it didn’t, that was me making a start trying to get my plan together and prepping it to be attached.

Ok got you, you probably know a lot more than me tbf.
And yes by the way, it is an ITC 1000 F (had to check).

I’m gonna read up a bit more about relays, but I think what you’re saying makes sense (and yeah will swap out for the other colour wires in that case to keep it all logical as poss)
 
I agree with @Slimmct that what you have there are relays, think of them as electronic switches that join 5 to 6, and 7 to 8.

BUT you need to use 2 for live and 1 for neutral as per picture below.
You want the relay or switch on the live side of the connected loads, otherwise they will have 230v at them even when turned off, as you would be turning them of by removing the neutral.
Just as in a domestic lighting circuit you wouldn't want the bulb-holders live when the lights are off - same principle.

(If you don't understand my last sentence then respectfully don't proceed and get some help.)

There are also several more things to think about:
The relays are rated at 10A, so you wouldn't be able to put a 13A fused plug on the power supply, it would need to be 5A or 10A fuse in the plug. The flex you use throughout would need to need to be minimum 1mm sq. csa to carry 10A.
You also need to consider the power consumption of any loads you intend to plug in and ensure they don't draw more current than 10A.

Finally, yes, it's important to connect the earths from the supply flex to the other two earths.

There is potential for short circuit, electric shock and even fire if this isn't done correctly so please get some local help if you are not confident you can do it safely.

[ElectriciansForums.net] Join earth wires (from 3 power cables)  together when wiring temperature controller (ITC 1000)?
 
I agree with @Slimmct that what you have there are relays, think of them as electronic switches that join 5 to 6, and 7 to 8.

BUT you need to use 2 for live and 1 for neutral as per picture below.
You want the relay or switch on the live side of the connected loads, otherwise they will have 230v at them even when turned off, as you would be turning them of by removing the neutral.
Just as in a domestic lighting circuit you wouldn't want the bulb-holders live when the lights are off - same principle.

(If you don't understand my last sentence then respectfully don't proceed and get some help.)

There are also several more things to think about:
The relays are rated at 10A, so you wouldn't be able to put a 13A fused plug on the power supply, it would need to be 5A or 10A fuse in the plug. The flex you use throughout would need to need to be minimum 1mm sq. csa to carry 10A.
You also need to consider the power consumption of any loads you intend to plug in and ensure they don't draw more current than 10A.

Finally, yes, it's important to connect the earths from the supply flex to the other two earths.

There is potential for short circuit, electric shock and even fire if this isn't done correctly so please get some local help if you are not confident you can do it safely.

View attachment 85637
Really appreciate all the detail. Going to take a step back before going any further. There’s so many videos of people doing this but all different and in different countries hence I wanted to double check I understood correctly!
 
I agree with @Slimmct that what you have there are relays, think of them as electronic switches that join 5 to 6, and 7 to 8.

BUT you need to use 2 for live and 1 for neutral as per picture below.
You want the relay or switch on the live side of the connected loads, otherwise they will have 230v at them even when turned off, as you would be turning them of by removing the neutral.
Just as in a domestic lighting circuit you wouldn't want the bulb-holders live when the lights are off - same principle.

(If you don't understand my last sentence then respectfully don't proceed and get some help.)

There are also several more things to think about:
The relays are rated at 10A, so you wouldn't be able to put a 13A fused plug on the power supply, it would need to be 5A or 10A fuse in the plug. The flex you use throughout would need to need to be minimum 1mm sq. csa to carry 10A.
You also need to consider the power consumption of any loads you intend to plug in and ensure they don't draw more current than 10A.

Finally, yes, it's important to connect the earths from the supply flex to the other two earths.

There is potential for short circuit, electric shock and even fire if this isn't done correctly so please get some local help if you are not confident you can do it safely.

View attachment 85637

Right I’ve gone over what you have said again.
Totally appreciate your comments about which terminals each wire should go to etc. All makes sense.

With regards to amps and cable size... assuming if I change the plug going into mains from a 13amp to 10amp this will ensure the circuit isn’t overloaded from the mains.

Presumably the cable that was previously attached to a 13amp plug is all good to go for a 10amp plug (as I understand it the minimum is the issue rather than it being a bit bigger?)
 
Presumably the cable that was previously attached to a 13amp plug is all good to go for a 10amp plug (as I understand it the minimum is the issue rather than it being a bit bigger?)
That should be the case, yes. You should check though.

To be clear the reason I made a big deal of the connections was that your photograph showed the live and neutral one way, the helpful post by @Slimmct described it in a way that would work but didn't match the diagram sticker on the top.
I thought it best if you had everything consistent so the sticker was representative of the arrangements.
 
That should be the case, yes. You should check though.

To be clear the reason I made a big deal of the connections was that your photograph showed the live and neutral one way, the helpful post by @Slimmct described it in a way that would work but didn't match the diagram sticker on the top.
I thought it best if you had everything consistent so the sticker was representative of the arrangements.
Yeah I appreciate that! When I’ve watched videos they’ve said doesn’t matter if live or neutral goes in 1/2 but obviously sounds like a problem waiting to happen.

Ok so I’m going to go and get a 10amp plug to attach to mains, wire up as detailed by you above and should be golden. And in a worst case scenario something tries to draw too much power I assume the fuse on the mains supply plug will be the first thing to give out (which is the lesser of evils as I understand it)
 
That should be the case, yes. You should check though.

To be clear the reason I made a big deal of the connections was that your photograph showed the live and neutral one way, the helpful post by @Slimmct described it in a way that would work but didn't match the diagram sticker on the top.
I thought it best if you had everything consistent so the sticker was representative of the arrangements.

By the way, I took a step back to readmore and watch more about it before going ahead (and had other jobs to do)...

BUT I have since found this image on the Amazon page for the ITC 1000 (which actually has quite a lot of info).

In this image and the text it states live wire from power supply should go to port 1 and neutral to port 2. Everything else is exactly as you have suggested (thanks) but just thought I would add this info to this thread in case anyone else picks it up looking for guidance in the future.
 

Attachments

  • [ElectriciansForums.net] Join earth wires (from 3 power cables)  together when wiring temperature controller (ITC 1000)?
    F508BFAC-725A-4782-B2B9-A1948B5D3AEC.jpeg
    412.1 KB · Views: 36
Also I think this is the best video I have found so far, albeit for the STC 1000 which appears to have been made in same factory for a different brand haha..

*Although like most of the other videos he doesn’t bother changing supply to 10a plug instead of 13a plug which I’m still going to do to be safe as I have seen another video of a kid who used an ITC 1000 for gardening incubator moaning because he came in and it had melted

Pending work I should get to put this together finally tomorrow so will report back
 
Last edited:

Reply to Join earth wires (from 3 power cables) together when wiring temperature controller (ITC 1000)? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
228
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
687
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
645

Similar threads

  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3 4 5
Replies
68
Views
4K
  • Question
It's the policy on this forum not to give step by step advice. If you have an understanding of wiring requirements you will not have any...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top