Run into this today at a house my nephew is moving into....

[ElectriciansForums.net] Replacement of original Dolphin shower which also feeds pump

Original Dolphin 860 Shower (8600W) installed on 6mm Twin and Earth - maybe 15m length from the CU, which is an old MK board installed in 1986, but RCD protected - on a 45A MCB.

So far so 'normal'....

However, there is 2.5 T&E fed from the positive side of the valve, which feeds a pump in a cupboard above (via a FCU).

[ElectriciansForums.net] Replacement of original Dolphin shower which also feeds pump [ElectriciansForums.net] Replacement of original Dolphin shower which also feeds pump [ElectriciansForums.net] Replacement of original Dolphin shower which also feeds pump


They'd purchased a 9.5kW (@240) replacement, which I wasn't comfortable installing on 6mm cable given that the route is unclear - though mostly between floors I think , but the last part of it is in trunking down the wall to the fitting itself...

The pump is slightly throwing me too - it's clearly an old pump that works when turned on, so was fed from effectively a 'switched live' in the shower - fused with a glass fuse in the shower (FCU before pump above).

Is is possible/compliant to do this in any modern shower? Obviously many of them have electronic internals now anyway, so not always clear where a suitable feed could be taken.

Since there is a toilet next door with sink, which has hot water fed from a boiler, I suggested that they get a plumber to put a normal shower in instead....

Otherwise, It would seem that the way to do it properly now would involve changing the pump to one that has a trigger sensor?

On 6mm of 15-20m, I reckon they'd need 7.5kW (@240) - and that I should probably reduce the MCB to 30A (Old MK 3871 Type 2 board). Having said that, there is no obvious overload of the existing cable, which has been in since 1986 by the looks of it....

Does that sound right, or am I missing an obvious answer that is commonly done? Anyone replaced one of these in a similar situation?
 
It may be that the pump predates other changes to the plumbing, eg if boiler is now a combi it might be mains cold water now and the pump might not be needed.

If it still needs a pump, as well as an electric shower with a built in pump, the other option is a simple power shower with just the pump (e.g Mira Go), taking the hot and cold feed from the room next door as suggested. Only 3 amps too then!
 
It may be that the pump predates other changes to the plumbing, eg if boiler is now a combi it might be mains cold water now and the pump might not be needed.

If it still needs a pump, as well as an electric shower with a built in pump, the other option is a simple power shower with just the pump (e.g Mira Go), taking the hot and cold feed from the room next door as suggested. Only 3 amps too then!
From what I could see It's an older boiler, heating a tank (with back up immersion). Though the other shower in the property is fed normally with no pump that I could see, and as far as I know works fine....

Didn't check whether the water was mains or not now - or whether mains is available in the adjacent toilet... Will have to look into options with pumps, in case a plumber decides a normal shower isn't suitable....
 
From what I could see It's an older boiler, heating a tank (with back up immersion). Though the other shower in the property is fed normally with no pump that I could see, and as far as I know works fine...
Didn't check whether the water was mains or not now - or whether mains is available in the adjacent toilet... Will have to look into options with pumps, in case a plumber decides a normal shower isn't suitable....
It could be that the property has had low mains water pressure problems in the past which may have since been resolved. If you have 2 showers would the mains water pressure be sufficient to run both at the same time without any issues
 

Reply to Replacement of original Dolphin shower which also feeds pump in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

It's unlikely tht a small domestic garden pump and a single lamp will come anywhere near close to overloading even the smallest (3A) fused spur...
Replies
2
Views
369
  • Article
This is an RSS feed of thread: Why is my pumped shower suddenly slow in starting? Content of the thread: Not been on here for ages, got a lot of...
Replies
0
Views
185
  • Question
It’s quite common for an electrician to criticise another’s work as you will rarely get everything perfect.
Replies
20
Views
1K
  • Question
Better off with the click prw213 as it has twin screw termination.
Replies
9
Views
760
  • Question
Obviously you need to check the means of earthing, Ze, and polarity no matter what for the EIC. As above, if anything looks dodgy then EICR is a...
Replies
3
Views
548

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks